american standard compressor windings
what should the compressor windings ohm out at in an American Standard (Trane) [three phase] model # CSHC075R0A00? I am getting .47kOhms/351Ohms/97Ohms.
-
08-18-2012, 09:29 PM #2
They need to be even between all three legs. Make sure you test at compressor terminals without wires connected to get an accurate reading.
-
08-18-2012, 09:43 PM #3
-
08-18-2012, 09:53 PM #4
Regular Guest
- Join Date
- Aug 2012
- Location
- Statesboro, Ga
- Posts
- 6
those readings are with all wires removed and the breaker kicks off each time power is applied and the 208 leg was burned at the disconnect upon my arrival. I think the compressor is shorted and needs to be replaced but checking to be sure before I condem the part. thanks
-
08-18-2012, 09:56 PM #5
Your readings do not indicate a short.
.47kOhms actually qualifies as an OPEN winding in my book.
The problem may still be with the compressor, but you haven't provided enough information to determine for sure.
-
08-18-2012, 10:17 PM #6
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
-
08-18-2012, 10:23 PM #7
Those numbers seem kindof weird, maybe get an opinion from another meter? You should also check the CC heater to ground, if it has one. Also check each winding to ground.
BTW to address your question, usually you'll get .7 to 2 ohms between each winding.
-
08-18-2012, 10:24 PM #8
Regular Guest
- Join Date
- Aug 2012
- Location
- Statesboro, Ga
- Posts
- 6
those are the true numbers and I think the compressor is dead also but just wanted conformation
-
08-18-2012, 10:39 PM #9
Regular Guest
- Join Date
- Aug 2012
- Location
- Statesboro, Ga
- Posts
- 6
reading were done with a fieldpiece hs36 meter and checked multiple times to be sure accurate, as I stated earlier the pwr kicked at breaker box and 208 wire was burned at disconnect when I arrived, breakers and disconnect are good and so is contactor on unit, did every electrical ck I could think of and compressor windings were only thing out of wack and this is a 3 phase so should have been same on ea leg of compressor winding.
-