Dynamic AirFlow Troubles! Plz help
I am a Clean Room Specialists and am having some issues with a dynamic system which is being controlled by Price vav's at which are attempting to maintain a negative pressure and constant flow in a space. I have noticed at times that the DP varies although flows are being maintained and duct static pressures are maintained.
The system varies from -.06(ideal) to -.09(life safety concern) however like I said the flow rates have negligible change no more than about 35cfm on a system that flowing 1200cfm. When the system pressure gets upwards of -.09 we have door closing issues. Any suggestions or information would be helpful.
Thanks
BB
-
08-06-2012, 10:34 PM #2
-.09(life safety concern)???
There is more of pressure loss going from 0' elevation to 500' elevation.
-
08-07-2012, 05:58 AM #3
New Guest
- Join Date
- Aug 2012
- Posts
- 2
Its been determined that once the space starts to hit a -.1 it takes upwards of 60lbs of pull to open the door. In case of an emergency its a concern on whether a 4'10" 90lbs young lady can open the door or not.
-
08-07-2012, 06:06 AM #4
A 3'X7' door with a negative pressure of .1" holding it shut, would only have a total of 10.8 pounds of force against it.
-