High side pressure fluctuates on new system.
I just installed a new Goodman 13SEER 2.5Ton R410a (scroll) fixed orifice system with new air handler. Correct oriface was installed. Out side temp is 93F indoor is 73F. Low side pressue fluctuated 132-136psi. Low side temp is 58.6F giving me a superheat of 17.4. Calculated super heat is 14. Not far off. The high side is fluctuating from 450-650psi. I have not seen this before. I can hear the compressor labor at the higher pressure. My boss said not to worry about it unless the customer calls. I think the compressor may be damaged by this high pressure. Any thoughts out there?
-
08-17-2012, 07:47 PM #2
Professional Member*
- Join Date
- Jul 2010
- Location
- nebraska
- Posts
- 1,168
Shouldn't have anywhere near that high of head pressure with 93 ambient. If you weighed in the correct charge then check for non condensables.
-
08-17-2012, 08:16 PM #3
Might as well get some parts in stock now.
Always here
-
08-17-2012, 09:00 PM #4
You have a 5mm coil unit. You need to remove some.
-
08-17-2012, 09:33 PM #5
Sounds like noncondensables to me. Did you pull deep vacuum? Microns?
-
08-17-2012, 10:07 PM #6
Professional Member
- Join Date
- Jun 2012
- Location
- St. Cloud, MN
- Posts
- 25
Balance the charge, all I install is Goodman and I've seen this more times than I can count.
Last edited by cavitech; 08-17-2012 at 10:08 PM. Reason: Suspect.
-
08-18-2012, 07:07 AM #7
Remove some and tell us what happens ....
-
08-18-2012, 09:18 AM #8
Regular Guest
- Join Date
- Nov 2011
- Location
- USA
- Posts
- 186
For that OD temp, the head pressure should be around 375 psi. Measure subcooling and see if it's not way high.
-
08-18-2012, 09:49 AM #9
Overcharged
-
08-18-2012, 10:24 AM #10I agree, first glance sounds like noncondensables
Originally Posted by socotech
-
08-18-2012, 09:09 PM #11
Professional Member
- Join Date
- Apr 2008
- Location
- warwick, ny
- Posts
- 39
Not to sound stupid but from what i read he has a new 410a system and a new air handler,Shouldnt that be a txv not a fixed orifice.
and did he change the filter drier as well
-
08-18-2012, 09:26 PM #12
They ship systems with orifices and txvs. If was new system why wasn't the factory charge adequate?
-
08-18-2012, 10:38 PM #13