Results 1 to 13 of 24
    Aug 2012
    Confused High side pressure fluctuates on new system.
    I just installed a new Goodman 13SEER 2.5Ton R410a (scroll) fixed orifice system with new air handler. Correct oriface was installed. Out side temp is 93F indoor is 73F. Low side pressue fluctuated 132-136psi. Low side temp is 58.6F giving me a superheat of 17.4. Calculated super heat is 14. Not far off. The high side is fluctuating from 450-650psi. I have not seen this before. I can hear the compressor labor at the higher pressure. My boss said not to worry about it unless the customer calls. I think the compressor may be damaged by this high pressure. Any thoughts out there?
    Jul 2010
    nebraska
    Shouldn't have anywhere near that high of head pressure with 93 ambient. If you weighed in the correct charge then check for non condensables.
    Delaware
    Might as well get some parts in stock now.
    Always here
    Tallahassee, FL
    You have a 5mm coil unit. You need to remove some.
    Nov 2007
    Mississippi
    Sounds like noncondensables to me. Did you pull deep vacuum? Microns?
    Jun 2012
    Minnesota
    Balance the charge, all I install is Goodman and I've seen this more times than I can count.
    Virginia
    Remove some and tell us what happens ....
    Nov 2011
    For that OD temp, the head pressure should be around 375 psi. Measure subcooling and see if it's not way high.
    Oct 2010
    Overcharged
    Dec 2008
    Ontario Canada
    Quote Originally Posted by socotech
    I agree, first glance sounds like noncondensables
    Apr 2008
    Greenwood Lake, ny
    Not to sound stupid but from what i read he has a new 410a system and a new air handler,Shouldnt that be a txv not a fixed orifice.
    and did he change the filter drier as well
    Jun 2012
    East tx
    They ship systems with orifices and txvs. If was new system why wasn't the factory charge adequate?
    Dec 2010
    Palm Beach,Fl.
    If its a microchannel condenser the charge will be very light for even the shortest runs and in general will hold almost 20% less than a comparable tube/fin system when fully charged.
    Quote Originally Posted by k-fridge View Post
    The laws of physics know no brand names.