  1. #79
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by udarrell View Post
    Yep, it definitely indicates it is a high pressure reset button; which means something else is happening to trip it...
    Like what, for instance?

  2. #80
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 10-06-2012 at 02:00 PM. Reason: Non Pro * Member

  3. #81
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503

    Moderator.... a little help here, please!

    Quote Originally Posted by Workin4TheMan View Post
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    No offense, but you're not an asterisked pro member, so please stop responding to my posts.... leave it to the pro's, please!

    BTW, refrigerant pressures/temps were checked and double-checked by the tech when he repaired leaks and replaced the accumulator two months ago. Since then, except for the reset issue related to filter change, the system has been cooling better than ever.
    Last edited by beenthere; 10-06-2012 at 02:02 PM. Reason: Removed quote of Non Pro * Member

  4. #82
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by Workin4TheMan View Post
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    You may be funny, to some, but you're not helping me at all.

    No offense, but you're not an asterisked pro member, so please stop responding to my posts.... leave it to the pro's, please!
    Last edited by beenthere; 10-06-2012 at 02:03 PM. Reason: Removed quote of Non Pro * Member

  5. #83
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 10-06-2012 at 02:00 PM. Reason: Non Pro * Member

  6. #84
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,789
    Workin4TheMan, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.
    Further infractions may result in loss of posting privileges.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #85
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,981
    Could be bad txv, trash in the metering device, partially blocked filter drier, bad pressure switch, gremlins or ghosts in the machine. It needs to be thoroughly checked or more damage may be being done.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  8. #86
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,773
    The air filter shouldn't have anything to do with a high head preasure trip unless the unit is in heat mode. In ac it could be dirty condenser coil, weak or stopping condenser fan motor, overcharged with refrigerant, or a restriction in the refrigeration circuit. It's odd that it seems directly correlated with a filter change.

  9. #87
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by jtrammel View Post
    The air filter shouldn't have anything to do with a high head preasure trip unless the unit is in heat mode. In ac it could be dirty condenser coil, weak or stopping condenser fan motor, overcharged with refrigerant, or a restriction in the refrigeration circuit. It's odd that it seems directly correlated with a filter change.
    Odd, indeed. The condenser fan is running strong, with lots of hot air exhaust. I put my hand on the compressor housing and it's not hot. BTW, it was hot when the switch tripped after the filter change, both with the Honeywell MERV 10 and the MERV 11. The coil fins are quite corroded, but no dirtier than usual. I'm afraid if I try to run a hose through the coil the fins will fall off. Yes, I do know the coil has to be rinsed from the inside out.

  10. #88
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by dan sw fl View Post
    a 1" MERV 11 could probably ' trip me out' from 200 miles away.

    Not sure of the specific impact from a 4" MERV 10.
    I would Not use more than a MERV 8 in any case.

    If I had health issues, I'd get a portable HEPA unit, that way both me and my equipment can survive.
    I'll stick with the MERV 8 for the time being. No real health issues, but too much dust, pollen, etc. does make me sneeze and aggravates my post nasal drip (side effect from blood pressure meds). So far, haven't had that problem inside my house.

    But I'd like to know what 3-ton equipment you have in your home that gets you a high bill of $130? Your house is close to mine in square footage (~1800). I'm home alone most of the time and don't use many appliances, but my high bill in mid-August is $250, at about 74 kWh/day. My low bills in mid-December and mid-February are $60 each, at about 19 kWh/day.

    My high bill in VA every year, over the 7 years I lived there, was $130 in a 2200 sf 3-story townhouse. I sure would like to see bills like that again!

  11. #89
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    5,033
    Quote Originally Posted by jtrammel View Post
    The air filter shouldn't have anything to do with a high head pressure trip unless the unit is in heat mode.

    In ac it could be dirty condenser coil, weak or stopping condenser fan motor, overcharged with refrigerant, or a restriction in the refrigeration circuit. It's odd that it seems directly correlated with a filter change.
    Since you're running it in the cooling mode; jtrammel is on target, except for some restriction exceptions which though usually high, depending on where located, some locations cause the system to pump down.

    Maybe it is getting attic air leaked into the return air; then a clean filter would allow an increased evaporator airflow heat-load to possibly trip the head pressure shut-down; it's even more apt to happen, due to hot moisture loaded attic air, if the system is overcharged or has a lot of non-condensibles in the refrigerant system.
    Last edited by udarrell; 10-06-2012 at 04:57 PM. Reason: Skewed meaning(s)...

  12. #90
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,981
    Quote Originally Posted by Florida Joy View Post
    Odd, indeed. The condenser fan is running strong, with lots of hot air exhaust. I put my hand on the compressor housing and it's not hot. BTW, it was hot when the switch tripped after the filter change, both with the Honeywell MERV 10 and the MERV 11. The coil fins are quite corroded, but no dirtier than usual. I'm afraid if I try to run a hose through the coil the fins will fall off. Yes, I do know the coil has to be rinsed from the inside out.
    I think you found your problem. If the aluminum fins are eroded, the outdoor coil is not removing enough heat and the head pressure is going up. The only way to be certain is to have the system professionally tested.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  13. #91
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,505
    Quote Originally Posted by Florida Joy View Post
    I'll stick with the MERV 8 for the time being. No real health issues, but too much dust, pollen, etc. does make me sneeze and aggravates my post nasal drip (side effect from blood pressure meds). So far, haven't had that problem inside my house.

    But I'd like to know what 3-ton equipment you have in your home that gets you a high bill of $130? Your house is close to mine in square footage (~1800). I'm home alone most of the time and don't use many appliances, but my high bill in mid-August is $250, at about 74 kWh/day. My low bills in mid-December and mid-February are $60 each, at about 19 kWh/day.

    My high bill in VA every year, over the 7 years I lived there, was $130 in a 2200 sf 3-story townhouse. I sure would like to see bills like that again!
    If the bill is only $130 on a 3 ton unit either the person has low electric rates or an oversized AC unit. Figure 12+ hrs per day run time in a peak month for a properly sized unit at a 3,000Watt draw. The AC alone would use 1080KWH per month if sized to run 12hrs per day in a peak month. At 10 cents per KWH that's $108 for AC alone. This doesn't include any other use in the house or the base meter charges/taxes/fees.

Page 7 of 11 FirstFirst 1234567891011 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event