Thread: Any benefit to adding 5-inch media filter when new system is installed?

  1. #1
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    504
    Post Likes

    Any benefit to adding 5-inch media filter when new system is installed?

    I've been using 3M Filtrete Filters to help with my dust/pollen sensitivity, either their MPR 1000 (Merv 11) or MPR 1500 (Merv 12), depending on what's on sale at BJ's or Sam's Club. Current system is 3.5 ton Rheem, 12 years old, struggling to maintain t-stat temps since the condenser bottom rusted and fell out and the coil fins have extensive corrosion. I'm looking into replacing the system with either an inexpensive 3.5 ton single compressor system, or going with the top of the line Trane XL20i.... 3 or 4 ton depending on Manual J load calc.

    My question is this: Is there any benefit to adding a 5-inch media filter to the a/h?

    One quote I received offers a "free" 5-inch media filter as part of the Trane installation. The extra 7 inches required to install the filter cabinet will require lowering the stand that my a/h sits on, which may require patching drywall or adding 2x4's or some such to repair the wall above the new, lower a/h stand. Without the media filter cabinet, there's enough space for the new a/h without changing the stand. This contractor's quote included the Trane 900 t-stat. I've since seen the Trane 950 t-stat and it's AMAZING to a geek like me! I'm thinking about asking if he'd consider dropping the "free" media filter and including the 950 t-stat instead.

    Besides, if I use the media filter, I suppose I'd have to change it every so often and I understand replacement filters are quite expensive compared to the paper filters.

    What do you all think?

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    A 5" pleated filter is much better than any 1" filter, especially the so called "high efficiency" ones for a couple of reasons.

    For one, the 5" filter is way better for the overall operation of your entire HVAC system because it will not restrict airflow the way a 1" filter will do. At the same time, because of how much more surface area there is, a 5" filter will capture more airbourne contaminants due to a slower air flow rate across the filter.

    Just make sure the contractor has a good air seal around the perimeter of the filter, the filter has a well sealed door/panel over it and that there are absolutely no openings whatsoever between the filter and the system blower wheel. That means screw holes, connections....anywhere that any amount of air can enter the system without being filtered.
    Training is important!
    Practical Training is a must!

  3. #3
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    There is more surface area on the filters so they help with static pressure issues. That also means they should take longer to plug up, I personally would take the filter.

  4. #4
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    I guess roboteq hit enter first lol

  5. #5
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    If duct is not sized properly for a 3m 1" filter or any restrictive filter for that matter it raises the blood pressure of the entire system (ESP!!!!) can cause harm to entire system. The 5" filters require less frequent changes due to the surface area of the media usually only once or twice a year.

  6. #6
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    504
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    If duct is not sized properly for a 3m 1" filter or any restrictive filter for that matter it raises the blood pressure of the entire system (ESP!!!!) can cause harm to entire system. The 5" filters require less frequent changes due to the surface area of the media usually only once or twice a year.
    I guess i should have included additional info regarding the air return and the Filtered Grill/Grills feeding the return. The return is a ductboard sealed space directly under the a/h stand measuring 36 wide x 30 high x 26 deep which currently is fed by a 20 x 20 filtered grill through the hall wall. They will add another 20 x 20 filtered grill through the foyer wall.... the a/h sits in the corner of my laundry... the hall wall meets the foyer wall at a 90 degree angle and the a/h is directly on the other side of the wall in that corner.

    Wouldn't the planned 2 filter grill returns obviate the need for the media filter? They'll remain filtered regardless... would that be a problem?

  7. #7
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Quote Originally Posted by Florida Joy View Post
    I guess i should have included additional info regarding the air return and the Filtered Grill/Grills feeding the return. The return is a ductboard sealed space directly under the a/h stand measuring 36 wide x 30 high x 26 deep which currently is fed by a 20 x 20 filtered grill through the hall wall. They will add another 20 x 20 filtered grill through the foyer wall.... the a/h sits in the corner of my laundry... the hall wall meets the foyer wall at a 90 degree angle and the a/h is directly on the other side of the wall in that corner.

    Wouldn't the planned 2 filter grill returns obviate the need for the media filter? They'll remain filtered regardless... would that be a problem?
    No its not a problem if you don't want it. I recall in another thread that you were concerned your ducts wouldn't be sufficient for a larger ton system if you couple that with the 3M 1" filters then your external static pressure is going to be too high for design. Unless your duct system is designed for a 3M filter it is going to raise your esp on system and cause premature failure. A 5" filter will be much less restrictive. They also make 5" filters that fit into filter grilles.

  8. #8
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    504
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    If duct is not sized properly for a 3m 1" filter or any restrictive filter for that matter it raises the blood pressure of the entire system (ESP!!!!) can cause harm to entire system. The 5" filters require less frequent changes due to the surface area of the media usually only once or twice a year.
    But I see a problem in lowering the a/h stand... perhaps as much as 10 inches to fit the filter cabinet and provide "working space" during shortening of the plenum above the a/h to accommodate the extra height of the new a/h. Lowering the stand that much would cover a few inches of the 20 x 20 grills and reduce airflow.

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    i agree, i would ask if instead of the filter at the furnace to put two 5" filters in the filter grilles themselves.

  10. #10
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Filters in filter grilles need to be larger than do filters located directly onto the unit due to the static pressure of the ducting between the filter grill and the blower section. There is also a reduction of free air area with the filter grill louvers. As long as there is enough free area of filter grill and all air passages from the filter grills and the blower section are completely sealed, filter grills are fine.

    No matter what, 5" filtes are going to be much better than 1" filters. If you use 1" filters, it is best to use the least expensive fiberglass filters and make sure there is a good air seal around them.
    Training is important!
    Practical Training is a must!

  11. #11
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    504
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    No its not a problem if you don't want it.
    What I meant was, would having all 3 filters be a problem... the 5" filter in the Trane cabinet AND two 20 x 20 Filtrete paper filters?

    Quote Originally Posted by jtrammel View Post
    I recall in another thread that you were concerned your ducts wouldn't be sufficient for a larger ton system if you couple that with the 3M 1" filters then your external static pressure is going to be too high for design. Unless your duct system is designed for a 3M filter it is going to raise your esp on system and cause premature failure. A 5" filter will be much less restrictive.
    'T'wasn't I who was concerned... I still feel confifdent they'd be sufficient... it was the pro's in this forum who insisted my duct system couldn't possibly be adequate and recommended that I hire the services of an air balancing specialist to confirm their suspicions. I'll continue my efforts to have that done before opting for a 4 ton replacement... but the decision on 3 versus 4 ton hasn't been made yet.

    Quote Originally Posted by jtrammel View Post
    They also make 5" filters that fit into filter grilles.
    I guess that would require changing out my 1" filter grill to a 5" filter grill. Didn't know that... I'll have to look into it. Thanks!
    Last edited by Florida Joy; 08-17-2012 at 04:19 PM. Reason: spelling

  12. #12
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Quote Originally Posted by Florida Joy View Post
    What I meant was, would having all 3 filters be a problem... the 5" filter in the Trane cabinet AND two 20 x 20 Filtrete paper filters?
    Yes of you use filtrete filters in the grilles. If you use cheap fiberglass in grilles probably not



    'T'wasn't I who was concerned... I still feel confifdent they'd be sufficient... it was the pro's in this forum who insisted my duct system couldn't possibly be adequate and recommended that I hire the services of an air balancing specialist to confirm their suspicions. I'll continue my efforts to have that done before opting for a 4 ton replacement... but the decision on 3 versus 4 ton hasn't been made yet.
    Sorry, my mistake


    I guess that would require changing out my 1" filter grill to a 5" filter grill. Didn't know that... I'll have to look into it. Thanks!
    no the 5" filters are made to fit in a regular filter grille

  13. #13
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    504
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    no the 5" filters are made to fit in a regular filter grille
    Hey, thanks jt! I just did some googling and found out how that works. There are a number of mfg making the 1-inch flanged 5-inch deep filters that fit a standard filter grill, for example:

    http://www.ventingdirect.com/smart-f...ilter/p1816562

    So.... I've decided against the "free" 5-inch media filter and the 7-inch Trane cabinet that it slides into.

  14. #14
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    504
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    no the 5" filters are made to fit in a regular filter grille
    I wonder why I've never heard of this until now? Here's a cool video showing how it's done!

    http://www.youtube.com/watch?v=sOJ0dte_z-Y

  15. #15
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    Quote Originally Posted by Florida Joy View Post
    I wonder why I've never heard of this until now? Here's a cool video showing how it's done!

    http://www.youtube.com/watch?v=sOJ0dte_z-Y

    yuup. they are excellent, and they clean the entire duct system, not just the equipment.
    I've been selling them for years. I love them. I use the honeywell series fc40
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  16. #16
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by vstech View Post
    yuup. they are excellent, and they clean the entire duct system, not just the equipment.
    I've been selling them for years. I love them. I use the honeywell series fc40
    Correction; filter grills "keep" entire duct system from getting dirty....IF THE DUCT SYSTEM IS COMPLETELY SEALED OF ALL AIR INFILTRATION POINTS!

    Two things that must be considered when using filter grills:


    1. Duct system needs to be sealed, air tight, throughout the entire system between the filter grill and the system blower. This means that every connection, screw hole etc. must be either sealed with a sealant or taped...or both, to prevent ANY amount of air being drawn into the system without having to pass through the filter.
    2. A filter grill must be larger than a filter installed at the air handler/furnace. The static pressure drop of the ducting and the free area space of the filter grill must be taken into consideration for proper filtration. The surface area of a typical filter grill needs to be about 40% larger than that of a filter located at the blower source.
    Training is important!
    Practical Training is a must!

  17. #17
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    FIRST and most important fact is __ NEVER USE FILTRETE ! or any filter more than MERV 7 which creates an initial dP >0.2".
    You're asking for problems created by very low air flow in many/most situations ! !!


    5 inch filter should last AT Least a Year.

  18. #18
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    FIRST and most important fact is __ NEVER USE FILTRETE ! or any filter more than MERV 7 which creates an initial dP >0.2".
    You're asking for problems created by very low air flow in many/most situations ! !!


    5 inch filter should last AT Least a Year.
    Higher MERV rated filters are fine as long as they have enough surface area to not cause issues with air flow. The most restrictive filter "can" be just fine as long as it is large enough. Unfortunately, with some of these filters on the market, they would have to be five times as large as they are to not cause air flow issues.

    How long a filter lasts is completely up to the conditions of each individual home. A filter that barely gets dirty after a year in one home can very well be needed to be changed within a month in another home. With 5" filters, I always suggest checking them quarterly for the first year to determine how well they are going to do over time.
    Training is important!
    Practical Training is a must!

  19. #19
    Join Date
    Oct 2004
    Location
    Palm Desert home, Bear Valley Springs home & Maui condo
    Posts
    4,126
    Post Likes
    Another note on filter grilles. Returns need to be ducted to use a filter grille. Loose framed chases or wall cavities are a bad choice for a filter grille. I usually move the filter to the unit when I run across these situations.

    I run Aprilaire media filters on both of my units. I have sheading dogs who love to lay near the return. 2-3 months is about it here.

  20. #20
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    What I meant was, would having all 3 filters be a problem... the 5" filter in the Trane cabinet AND two 20 x 20 Filtrete paper filters?
    If U use filters in the conditioned areas or in the Return ducts, U should not use a filter in the furnace/air handler; - double filtering increases the static pressure way too much.

    Two large filter racks in the conditioned area with the deep filters will do a great job filtering, along with being very efficient.

    Yes, the returns are best ducted...
    Last edited by udarrell; 08-18-2012 at 02:42 PM. Reason: Typos...

Page 1 of 7 1234567 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •