08-17-2012, 05:23 PM #14
Professional Member*
- Join Date
- Apr 2006
- Location
- Barrie Ontario
- Posts
- 192
You can't vent on the side if it's a zero lot line you need to find another option I would also recommend the chase
-
08-17-2012, 05:49 PM #15
Regular Guest
- Join Date
- Aug 2012
- Posts
- 8
This sounds promising. What is involved in "opening up the chimney base"? i.e.: Do you mean masonry work to increase the width of the chimney (sounds expensive).
Also, have you had any issues with frost forming on the opening of the exhaust? It sounds like your climate would be similar, although a bit warmer, to mine (Toronto, Canada).
-
08-18-2012, 04:24 PM #16
-
08-18-2012, 09:49 PM #17
Professional Member*
- Join Date
- Dec 2010
- Location
- Toronto
- Posts
- 1,252
There is no problem taking the combustion air from the side and running the 3" 636 PVC up the chimney (last time I checked 2" was not allowed in Ontario for this boiler, but they were trying to get it passed). I have done it many times. That said, lots of people will vent out 7 ft above grade in Toronto and because venting can be a bit tough in the city, sometimes it is accepted. I am not advocating it but it has happened and been accepted (not by TSSA but by some local young fitter that is sent out by Enbridge).
Your best bet is the Viessmann 100 with the DHW package vented up the chimney then seal up the chimney, top and bottom.
Stay away from those other boilers you mentioned. They pale in comparison.
-
08-18-2012, 11:33 PM #18
Professional Member*
- Join Date
- Apr 2006
- Location
- Barrie Ontario
- Posts
- 192
If you do have it installed check the manual for the exhaust temp to make sure the PVC is acceptable product but im doubting it is most installers don't know or don't check
-
08-19-2012, 09:17 AM #19
Professional Member*
- Join Date
- Nov 2011
- Location
- Long Island, NY
- Posts
- 207
Innoflue
I don't know about Canada, but in the US we have been using 2" pp to vent the Vitodens 100. The 2" ridged slides right down the chimney no problem. Placing the intake near the driveway shouldn't be a problem (as long as it's above the snow line).
-
08-19-2012, 12:45 PM #20
We are licensed for steam and hot water in Minneapolis and factory trained (BC school) for Viessmann Solar and Vitodens. We also have installed many Viessmann boilers vented to or across the driveway. It is not a public path and rarely used as a sidewalk. The Viessmann makes one of the best concentric (co-axial) vent kits on the market today. The kit may use an existing "B"vent, masonry or new chase with zero clearance to combustibles. The coax also assure sealed combustion and direct -vent with the added advantage of pre-heating the intake combustion air. This has come in handy in high altitude or extreme weather installations. The coax vent is also perfect for side venting through a rim-joist with little chance of frosting or cross-contamination.
Extending a vent beyond the exterior must be done with caution since the water vapor can freeze up the vent if the vent is cooled too long before hitting the open air. I know of know condensing boiler manufacturer that will allow a 7 foot flue extension beyond the envelope...