i didnt mean that i wnt to swap the 22 with 410a by changing the split unit freaon only
i meant changing the whole 22 split unit with new split working on 410a
when we tried the 410a new split their cooling was not so good since the temp is reached 55c in some places
also 22 freon cooling is very good but the conpressor is overheated then stopped working
so do you advice me to use freon 407c or not
thanx
-
12-08-2012, 01:16 PM #30"Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted
-
12-08-2012, 01:22 PM #31
thanx
ok
what is opinion if i use new split unit working on 407c
is freon 407c is best than r22
-
03-08-2013, 10:31 PM #32
New Guest
- Join Date
- Mar 2013
- Posts
- 2
most air conditioning systems are designed for 90 degree ambient,for proper operation situations. clearly you are exceeding that, you have add extra tonnage for the added temperature discrepency.
-
03-08-2013, 10:47 PM #33
New Guest
- Join Date
- Mar 2013
- Posts
- 2
basically just get a larger capacity condenser.
-
03-09-2013, 04:42 AM #34
-
03-09-2013, 09:50 AM #35
Water cooled is the only solution. You could rig up a lawn sprinkler spraying on the outdoor coil as a test. Saw that one time on a call. Stacked coil completely blocked.
Sent from my DROID RAZR using Tapatalk 2
-
03-11-2013, 07:34 AM #36
Professional Member*
- Join Date
- Oct 2002
- Posts
- 674
Water is more precious then R22 in the desert, isn't it?
-
03-11-2013, 08:43 AM #37
-
03-15-2013, 07:56 PM #38
If this is a thermal power plant, they have to have water available in order to make steam to run the turbines. The best bet, like others have said is probably a water-source ac or heat pump and a cooling tower. An air-cooled ac could work but not at stock specs. You would need a higher compression ratio to get the difference between high and low side to be greater. If you can get a walk-in to freeze in Phoenix (where I live), with an air-cooled system, you can get a room to room temp in 60 C ambient. But it has to be designed to do so. And 60-70C ambient is at the maximum temp of condenser fans. Highest I have seen is 70C rated which, if that is really ambient, by the time the air pics up condenser heat, it will be much warmer and probably cause a very short fan life. I would go with a WSHP.
-
03-19-2013, 07:37 AM #39
Professional Member*
- Join Date
- Oct 2002
- Posts
- 674
As posted earlier, different refrigerants have different "critical temperatures" that are less suitable to high temperatures. Any use of water to cool is complicated by minerals in the water. Typically, water in hot, arid climaytes is more problematic with fouling and if the hot climate is also very humid, there is little benefit to water cooling. Try to air cool, if all possible