Results 27 to 39 of 41
  1. #27
    Apr 2008
    Quote Originally Posted by KB Cool View Post
    Are you serious?
    Nah.
    I didn't think you were either.
    Just a nod of caution for the possibly unsuspecting..
    A close-up of the coil after a season or two would have been better.
  2. #28
    Jul 2011
    East coast USA
    Quote Originally Posted by mixsit View Post
    Nah.
    Interesting, yes i would be curious after a season how the coils look. in cold climates how much you want to bet it freezes, Because they forget its there...
  3. #29
    Iraq
    Quote Originally Posted by dlove View Post
    Thank YOU, i have been telling this to people and they just don't understand this. Over and over i have said when you replace a R22 with a 410 you may need re-size it because swapping out a 3ton r22 with a 3ton 410 will not operate the same in high temps.
    i didnt mean that i wnt to swap the 22 with 410a by changing the split unit freaon only
    i meant changing the whole 22 split unit with new split working on 410a
    when we tried the 410a new split their cooling was not so good since the temp is reached 55c in some places
    also 22 freon cooling is very good but the conpressor is overheated then stopped working
    so do you advice me to use freon 407c or not
    thanx
  4. #30
    Cincinnati, Oh
    Quote Originally Posted by kefah View Post
    thanx
    Thats exactly what he said.
    The system your trying to run is not designed to operate in the area you have it.
    You need a different type of system.
    Using ANY air source is not going to be effective.
    "Just get it done son."
    Dad adjusted
  5. #31
    Iraq
    thanx
    ok
    what is opinion if i use new split unit working on 407c
    is freon 407c is best than r22
  6. #32
    Mar 2013
    most air conditioning systems are designed for 90 degree ambient,for proper operation situations. clearly you are exceeding that, you have add extra tonnage for the added temperature discrepency.
  7. #33
    Mar 2013
    basically just get a larger capacity condenser.
  8. #34
    thanx
    ok
    R407C is not better the R22.
  9. #35
    Aug 2009
    Griffin, Georgia
    Water cooled is the only solution. You could rig up a lawn sprinkler spraying on the outdoor coil as a test. Saw that one time on a call. Stacked coil completely blocked.
    Sent from my DROID RAZR using Tapatalk 2
  10. #36
    Oct 2002
    Plano, TX
    Water is more precious then R22 in the desert, isn't it?
  11. #37
    Quote Originally Posted by timjimbob View Post
    Excellent observation.
  12. #38
    AZ
    If this is a thermal power plant, they have to have water available in order to make steam to run the turbines. The best bet, like others have said is probably a water-source ac or heat pump and a cooling tower. An air-cooled ac could work but not at stock specs. You would need a higher compression ratio to get the difference between high and low side to be greater. If you can get a walk-in to freeze in Phoenix (where I live), with an air-cooled system, you can get a room to room temp in 60 C ambient. But it has to be designed to do so. And 60-70C ambient is at the maximum temp of condenser fans. Highest I have seen is 70C rated which, if that is really ambient, by the time the air pics up condenser heat, it will be much warmer and probably cause a very short fan life. I would go with a WSHP.
  13. #39
    Oct 2002
    Plano, TX
    As posted earlier, different refrigerants have different "critical temperatures" that are less suitable to high temperatures. Any use of water to cool is complicated by minerals in the water. Typically, water in hot, arid climaytes is more problematic with fouling and if the hot climate is also very humid, there is little benefit to water cooling. Try to air cool, if all possible