Page 1 of 4 1234 LastLast
Results 1 to 13 of 41
    Iraq
    freon 410 problem in iraq
    hi iam working in thermal power plant
    we have about 200 split r22 unit
    4 ton.2ton and other and working very good
    but some times remp rises to 60 or 70 c in some rooms
    as so these unit stop working
    because of high ambient temp ( i heard the r22 max range is 53 c)
    so
    before a month we recieved new ac unit work on r410 as i know max temp range is 68 c
    problem is their cool effect was too weak >(not very cool")
    we thought problem may be from bad ac manufacturer
    so we tried another ac unit with same prob
    so waht u advice me to
    max summer temp in iraq reached 51 c
    Jul 2011
    East coast USA
    is this like a nuclear power plant...hummmmm...did you reset the red button?
    Not enough info, you offer not temps, pressures, Model #s so no one can help you.
    Maine
    I know R410a loses capacity at very high ambients, most compressors for R410a internally bypass at 600-650psi. At the high ambients your in I would bet the 410a internal bypasses are opening up. R22 is a little better in high ambients but the compression ratio can really get up there and shut the comps off on thermal. I'd call the manufacturer to see what they suggest.
    Maine
    Opps, didn't see the thermal power plant part, hope it's not nuclear
    Iraq
    Quote Originally Posted by dlove View Post
    its steam power plant
    as u know split unit normal suction pressure is 60 psi.when temp reaches 60 c
    pressure rise to 80 psi
    Tallahassee, FL
    Use the highest seer single stage heat pump unit you can.
    Why heat pump? They have much larger outdoor coil.
    But then again nothing is designed for what you describe.
    Iraq
    u mean its better
    if i use ac unit with cooling only
    no heat pump
    Southeastern Pa
    Quote Originally Posted by kefah View Post
    u mean its better
    no heat pump
    No, he means use a heat pump because the outdoor coil is larger.
    More information may allow some users here to give better advice.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Iraq
    thank u every one
    southeast
    Are you trying to say you are cooling some inside rooms at the plant that reach 60-70C when It's 51C outdoor. Or your trying to cool inside when it reaches 60-70C outside.
    Your R22 units are probably already under sized a bit for your outdoor temps. At your outdoor ambient temps, you should probably increase size by 1/2 to 1 ton when switching to R410A.
    Massachusetts
    You're given some very high numbers with limited information. For example, saying 60C to 70C is meaningless until you define the location of those temps. Normally for such a discussion, we'd need to have some idea of the indoor dry and wet bulb temps as well as the OAT. For example, if the indoor dry bulb is 60C and the OAT is 50C, then I'd first recommend a large dose outdoor air be circulated to reduce the indoor temps. Other questions I'd have would be about line length. Are you doing long lines applications? Capacity can be lost when using long lines. Standard conditions are not with what you're dealing here so I'd suspect you may need to have an engineered system, rather than off the line residential of light commercial units.
    Iraq
    Quote Originally Posted by coolinman View Post