Results 27 to 30 of 30
Thread: YORK YK CHILLER
-
08-30-2012, 11:16 AM #27
Professional Member
- Join Date
- Jan 2011
- Posts
- 647
If you mean refrigerant, I find that curious. If the pictures you sent were taken when the machine was at 88% FLA, it seems unusual to me that the evaporator small difference was 1.2*F. Usually the small difference temperature would be much greater in a low refrigerant charge situation.
Glad you solved your problem.
-
09-05-2012, 08:29 PM #28
-
09-05-2012, 08:32 PM #29
-
09-05-2012, 09:44 PM #30



Reply With Quote