Page 1 of 3 123 LastLast
Results 1 to 13 of 30

Thread: YORK YK CHILLER

  1. #1
    Join Date
    Aug 2012
    Posts
    13
    Post Likes

    YORK YK CHILLER

    Hi all,
    i m currently facing a problem on this YKDFDFP65CKF YORK CENTRIFUGAL CHILLER,
    when the chiller hit the setpoint 6.5c it cannot unload smoothly. it giving fluctuate reading on the display ( %FULL LOAD AMPS ) and continuous surging sound . The reading for chilled liquid temp- leaving at 6.5c, return at 11.6c, condenser liquid temp- leaving at 34.9c,return at 29.6c.Is there anyone here can give me some advice what going on and what must do. thank :anyone

  2. #2
    Join Date
    Jan 2011
    Posts
    1,582
    Post Likes
    What are the design conditions? Your conditions indicate it's a 10*F machine. Incidentally, since this is a USA based forum many will pass up questions that require they convert temperatures to fahrenheit. It would help if you converted them before you ask your question.

    If you go to the sales order screen it should tell you what the design conditions are. Generally speaking, when a machine starts surging the actual head has exceeded the design head. The other piece of information that may help is the small difference (approach) in the condenser and the evaporator. On the York Optiview they are reported as "small difference" on the evaporator and condenser screens.

  3. #3
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,235
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Incidentally, since this is a USA based forum many will pass up questions that require they convert temperatures to fahrenheit.
    Yeah, KnewYork's right, I'm one of those lazy ones...

  4. #4
    Join Date
    Aug 2012
    Posts
    13
    Post Likes
    Thread Starter
    My apologies. I'm situated in Singapore and all chillers' readings are in degrees celsius. Rather than explaining the issues in words, may i send you a video clip so that you can advice me appropriately? Chilled water leaving at 44F return at 53F, Condenser water leaving at 95F return at 85F!

  5. #5
    Join Date
    Jan 2011
    Posts
    1,582
    Post Likes
    I know what it's doing. It's surging. I've seen it countless times. I'm trying to figure out why. Take a picture of the sales order screen, the evaporator and condenser screens and post them here. That may be enough. By the way, I had done the conversions...I knew what was happening from that standpoint. Now I'm trying to find out what the chiller was designed to do and see if you may have a problem in the either of the shells. Where in the condenser sight glass is the liquid level being maintained?

    Also if you could go into the setpoints>setup screen and change the units from Celcius to Fahrenheit before you take the picture I, for one, would greatly appreciate it.

  6. #6
    Join Date
    Jan 2011
    Posts
    1,582
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Also if you could go into the setpoints>setup screen and change the units from Celcius to Fahrenheit before you take the picture I, for one, would greatly appreciate it.
    Actually, after logging in, go to setpoints>setup>user. Change the data display mode to English and the language to English (if it isn't already). That would help those of us who only speak English to help you.

  7. #7
    Join Date
    Aug 2012
    Posts
    13
    Post Likes
    Thread Starter
    Hi knewyork advice taken! Thank! I will post you ASAP!

  8. #8
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,750
    Post Likes
    There are a lot of things that could be going on post all the operating data so we can all look at it please and thank you.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  9. #9
    Join Date
    Aug 2012
    Posts
    13
    Post Likes
    Thread Starter
    http://www.youtube.com/watch?v=c6BWp9TemoA

    Hi all it a short video clips just check it out!!!

  10. #10
    Join Date
    Aug 2012
    Posts
    13
    Post Likes
    Thread Starter
    http://www.youtube.com/watch?v=M6n20f5ZmTw


    Hi all annoy the first video clip

  11. #11
    Join Date
    Jan 2011
    Posts
    1,582
    Post Likes
    Like I said a number of posts ago...I've heard many machines surge and filming the home screen doesn't do any of us any good in trying to determine what might be to blame for the surge. In addition, you didn't change the display units to English so we can see things in °F instead of °C. Incidentally, the surge is no where close to the worst I've heard. Actually, it's quite mild. Still can't help to find a solution until you provide operating DATA.

  12. #12
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,154
    Post Likes
    this is an interesting way to diagnose chiller problems...i hope that it doesn't catch on...i watch too much computer as it is.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  13. #13
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,750
    Post Likes
    Quote Originally Posted by jayguy View Post
    this is an interesting way to diagnose chiller problems...i hope that it doesn't catch on...i watch too much computer as it is.
    Pretty pictures nice sounds dosen't help much I guess we will be asking Siri whats wrong with my Chiller next !
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.