We've done a lot of geo systems and always size for heating at 98% factor. That is, the coldest weather 98% of the time. The bottom 2% is short term and can be handled with aux heating. That said, we always install either multiple 1-stage systems or 2-stage units to help accommodate the difference between winter heating and summer cooling. Cooling is generally about 50% of heating in our area. Now our prayers have been answer with modulating compressors. ClimateMaster now has a modulating unit and I'm sure others do or will shortly. With modulation, you can size for heating and easily accommodate all the cooling needs with good humidity control as well. I suspect 3-tons is the cooling load and 5-tons is the heating load, as stated by beenthere. As such, I'd go with the 5-ton systems, 2-stage or modulating. If you go 3-tons with a 5-ton heating load, you'll be paying a lot more for heat with the aux electric heaters. That's generally not the preference for geo systems.