    I've got two ground loop geothermal Cantherm 520's in Carlisle, MA. They provider heating, cooling and domestic hot water. I love that I don't have a combustion heating system, or noisy compressors outside. The Catherms are about 25 years old. I'm pretty sure I need to replace them, but with what? I'd prefer not to fall back to fossil fuel.

    The units can't keep up with cooling when it gets above about 80 deg F. They super-heat the hot water tank, which then trips the pressure valve and blows about 35 gallons of scalding hot water onto the basement floor. I'm routinely having to reset hi-pressure on the upstairs unit, but strangely not on the downstairs unit. The downstairs unit is forced air, while the upstairs unit runs liquid to blowers on second and third floors. Lots and lots of windows in this house.

    What would I replace these units with?

    Can the grounds loops be re-used?

    What are my options?

    All suggestions welcome.

    Regards,

    Troy

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    39,254
    Post Likes
    Sounds like a modern GSHP system(s) are in order. Do these things tie into your water heater? That's not good, best way is for them to heat a preheat tank. If these kept up in the past, then sizing is likely right but they may be tired.

    The ground loop is likely good though a smart geo guy should check flow, temps, etc. to rule out problems. If the loops are undersized, could be an issue too.

  3. #3
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    20,049
    Post Likes
    You can get two new geothermal units of you want and yes you should be able to use same loop. For some reason your unit has high head pressure though. Could be internal to the unit, water flow, or a number of things. Get a pro in goes to give you an estimate and INSPECTION to determine your probl. Good luck wish you the best

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    20,049
    Post Likes
    No insulation on water lines in attic maybe

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,911
    Post Likes
    Bet a good tech could find the problem with them and fix them.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    20,049
    Post Likes
    Quote Originally Posted by beenthere View Post
    Bet a good tech could find the problem with them and fix them.
    Agreed

  7. #7
    Join Date
    Aug 2012
    Posts
    3
    Post Likes
    Thread Starter
    Both units tie into the domestic hot water tank, which blows the hot water onto the floor when it gets too hot. The upstairs unit (that gets the hi-pressure light) also ties into a separate smaller water tank (a heat sink?) which feeds an additional bedroom over the garage that was added 7 years ago over the garage. This confuses me because that little baby hot water tank (a heat sync?) seems to be storing cold water (both in/out pipes are cold).

    I've only been in the house 2 years, so I don't know the whole story, but I suspect that the addition of the extra bedroom over the garage may have been too much load for the two Cantherms. The guy who designed the system is still around, and I think he is a genius and very nice, but I think he doesn't want to mess with it anymore.

  8. #8
    Join Date
    Aug 2012
    Posts
    3
    Post Likes
    Thread Starter
    I've had a couple of different service companies in, but I'm not yet comfortable that they understand the problem, or what the right solution might be.

    Thank you.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,911
    Post Likes
    Look for a company that specializes in geo's. What you describing sounds like a simple repair. Some older geo's don't have a good control system on the desuperheater, and can cause this when another problem occurs.
    Contractor locator map

    How-to-apply-for-Professional