Results 1 to 3 of 3
  1. #1
    Join Date
    Feb 2004
    Location
    Northern California
    Posts
    140
    Post Likes

    Daikin REYQ72MTJU, LC Fault Code

    Has anyone experienced an LC Fault Code on a Daikin VRV hooked up to a Daikin REYQ outdoor unit? In the service manual it says this is a "Malfunction of Transmission between Inverter and Control PC Board". I checked all connections but this is an intermittent problem so I'm not sure if I've solved the problem yet.

    Thank you!

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,623
    Post Likes
    It is unlikely to be the board since it is intermittent.
    Make sure the unit has a good ground, and that the grounds for the components in the unit are good.
    Make sure the control wiring between the boards in the unit are not routed against line voltage wires, especially the leads for the compressor.

    Basically, bad connection, bad ground, noise, or a bad board.

  3. #3
    Join Date
    Feb 2004
    Location
    Northern California
    Posts
    140
    Post Likes
    Thread Starter
    Mark,
    I did everything you advised and still had the problem so I changed out the main board on the master outdoor unit. It looks like I need to program the new board. Can this be done without additional software? I have the service manual and I'm reading up on how to use the LED's and buttons on the board but it doesn't quite make sense without some sort of display.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.