basic rule of thumb for filter area is MINIMUM of 200 square inches per ton of cooling.
you have 180.
I STRONGLY recommend getting the inches above 200/ton. I prefer 360/ton for long quiet filter life, and ability to use pleated filters.
DO NOT USE 1" PLEATED FILTERS with less than 300 square inches per ton.The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman
-
08-18-2012, 12:06 AM #15
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,616
also, blower noise is due to sound wave reflective surfaces in line with the openings.
if you install rough surface insulation in the blower compartment/plenum area and perhaps build air baffles that do not obstruct airflow, your noise will all but disappear!
how much room is there between the front of the air handler, and the doorjam?The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman
-
08-18-2012, 05:16 PM #16
Regular Guest
- Join Date
- Jun 2012
- Location
- Ft. Lauderdale, FL
- Posts
- 55
-
08-18-2012, 07:18 PM #17
Regular Guest
- Join Date
- Jun 2012
- Location
- Ft. Lauderdale, FL
- Posts
- 55
And does it still move 1600 cu.ft if the handler is set on the lowest fan speed, or would it be lower?
-
08-18-2012, 09:58 PM #18
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,195
would you not use ductboard with insulation facing inside closet to quiet and provide