OK i am not going to give you a textbook reply as you can read that in a book.
It can be confusing as it has changed from the S,Q,J,B series.
Basically it does have an ITP light but it does not work the same as the others. As soon as it goes into harvest the ITP light will stay on, then after harvest the ITP light will stay on for 6 mins solid in freeze while it is setting its thresholds. Just as stated you do not want to touch it in this 6 min period.
A good way i use it is when the itp on i do not touch it.
To read it you need to go
menu
service
Real time data
time & Temp
scroll down until you see 100hz & 120Hz range. This will give you a db reading next to it. Scratch the back pointy probe part and the numbers should go up.