08-13-2012, 01:26 PM #1
Are Filter/driers required on new installs
My brother just had a house built and I noticed there is no filter/drier on his ac. It is a brand new install. I brought this up to the general contractor and he told me it is not required on new installs. Assuming (and I know this is a big assumption) the lines were nitrogen purged while brazing and evacuated below 50 microns, this shouldn't be a big deal. However, I seem to recall manufacturers requiring their installation on new units. Couldn't find any requirement in the IMC. Anyone know if there is a code requirement or manufacturer requirement for a Filter/drier.
-
08-13-2012, 01:47 PM #2
Professional Member
- Join Date
- Mar 2011
- Posts
- 50
This is what the Ruud installation manual said. They actually provide a filter dryer with the unit- UPQL condensor.
As an added precaution, a high quality, bi-directional filter drier is recommend- ed to be installed in the liquid line, if not factory installed.
-
08-13-2012, 02:04 PM #3
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
08-13-2012, 02:20 PM #4
Look inside the unit to make sure its not there.
Sent from my ERIS using Tapatalk 2
-
08-13-2012, 02:39 PM #5
Goodman
-
08-13-2012, 02:40 PM #6
I will check.
-
08-13-2012, 04:10 PM #7
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
08-13-2012, 05:49 PM #8
-
08-13-2012, 05:57 PM #9
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
08-13-2012, 06:16 PM #10
His installers pull a vacuum below 50 microns??? Sure! Most RNC installers wouldn't know what a micron gauge is, some around us may not even use a vacuum pump judging from our findings
-
08-13-2012, 09:41 PM #11
I know, I have seen that too. That's what concerns me. Even saw a guy that had like 5 years of "experience" in commercial that didn't know how to use a vacuum pump. Of course his daddy also worked at the same company.
-
08-13-2012, 09:48 PM #12
I think all Goodman condensers come with a factory installed drier. I hate this because I don't have the option to pump down to replace. I like to move them outside the condenser after the first recovery.
-
08-13-2012, 09:51 PM #13
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251


Reply With Quote