    Trane Model Number YCCO60F1MOBE Problem

    Problem.....Compressor Is Sweating.

    5 Ton Trane Electric Cooling/Gas Heating.

    Conditions:
    83 Degrees Dry Bulb Outdoor Ambient.
    60 Pounds Suction Pressure.
    44 Degrees Suction Line Temperature.
    10 Degrees Super Heat.
    275 Pounds High Pressure.

    55 Degree Air Dry Bulb From First Supply Grille.
    84 Degree Air Dry Bulb At Return Air Grille.
    29 Degree Temperature Difference.

    Return consist of 2 - 20 X 25 X 1 RAFG.
    These 2 Grilles are in the ceiling of the structure.

    Evaporator Coil And Condenser Coils Are Very Clean!

    I would appreciate any advise of how to solve this problem.

    Thank You!!!!!

  2. #2
    Join Date
    Jul 2017
    Posts
    7
    Post Likes
    What's the sq footage of the building need more info!R/22 I assume.


    Sent from my iPhone using Tapatalk Pro

  3. #3
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    12,934
    Post Likes
    Quote Originally Posted by Rohoho22 View Post
    What's the sq footage of the building
    square footage means little to nothing
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

    Jtrammel - "I’m going to sell hvac systems derp derp derp"
    BBeerme - "every time he opens his mouth, he reminds me of a cow without the fart bag."

  4. #4
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    12,934
    Post Likes
    you dont have enough air flow
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

    Jtrammel - "I’m going to sell hvac systems derp derp derp"
    BBeerme - "every time he opens his mouth, he reminds me of a cow without the fart bag."

  5. #5
    Join Date
    Mar 2014
    Posts
    154
    Post Likes
    Thread Starter
    It is R22....I will have to get the building information.
    The system has 5 Amer-Flow Model Number 1500 W 14 14" Round Ceiling Diffusers. (Duct Size 14")
    It also has 2 - 6 Inch Round Celing Diffusers.....Model Number 1500 W. (Duct Size 6")

    While cleaning the evaporator coil today I observed the transition from the unit to the return duct was sheet metal 30" X 8" insulated inside with 1/2" duct liner. Thus reducing the duct dimensions to 29" X 7".....My ACCA Ductulator shows 810 CFM's for 29" X 7" metal duct @ .05 WC.....To beat it all, the 2 - 20" X 25" X 1" Return Air Filter Grilles leave their return boxes with a 14" Round Metal Duct (Each).....14" Round Pipe @ .05 WC shows 660 CFM's each X 2= 1300 CFM's. The entire return system is too small.

  6. #6
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    12,934
    Post Likes
    so, you have your answer

    replace the duct system or downsize the condenser/coil system.
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

    Jtrammel - "I’m going to sell hvac systems derp derp derp"
    BBeerme - "every time he opens his mouth, he reminds me of a cow without the fart bag."

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.