Results 1 to 4 of 4
  1. #1
    Join Date
    Aug 2012
    Posts
    1
    Post Likes

    UDATING BRYANT AIR HANDLER

    I have a 3 year old Bryant air handler model FA4CNF048 and serial number 2109A84797 that has a R22 TXV installed from the factory. My contractor says he will have to change the TXV to R410 and then extract the old R22 oil and then he will be able to install a new 4 ton 14 seer R410 condensing unit outside. He was not sure if he should replace the coil in the air handler or not. He says he will check with the factory. What suggestion do you have? My 12 year old compressor died the other day and needs to be replaced.
    Last edited by daisyduke; 08-15-2012 at 07:54 PM.

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    16,674
    Post Likes
    He can get a dry r22 outdoor unit and use same txv and coil. Unless you want 410a then best to change everything coil txv and line set ( copper connecting lines between indoor and outdoor)

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,608
    Post Likes
    I believe Bryant allows you to reuse their indoor coils(certain age range) when switching to R410A. Provided the metering device is changed out.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,031
    Post Likes
    First i would want to know that the coil does not leak ,as it could have leaked out the refrigerant and causing the compressor to run hot and die. I would replace the whole unit that way you will get 14 seer ,i think the existing air handler was for 10 and 12 seer units so you wont get 14 seer anyway

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.