    Aug 2012
    Palmyra MO
    Subcooling bouncing between 6 degrees and 15 degrees??
    Installed new compressor in a burnout situation on a walk-in beer cooler condensing unit. New HH suction line drier, l.l drier. My superheat was also bouncing between 15 degrees and 20 degrees. R-22. I made sure the bulb on the txv was tight and insulated properly. Will be doing a follow up on this unit tomorrow, but was just curious if the case being 50 degrees and a boat load of warm beer would cause this hunting.http://hvac-talk.com/vbb/images/smilies/cheers2.gif
    Anaheim, CA
    Your SH should fluctuate 8-12; 15-20 is telling me the TXV needs to be opened or just replace it to play it safe.
    Jul 2012
    Western KY
    Where is the bulb in reference to evap outlet?
    Aug 2012
    Palmyra MO
    Header on outlet vertical mount