Thanks, everyone, for your thoughts. I think the insulation isn't an issue but I'm going to inspect and confirm. I like the idea of determining flow rate from pressure diff, but I agree, it might be hard to pull off. I think I'm going to investigate the notion of air in the lines. That seems like a really promising avenue. Does anyone have any tricks for ensuring all the air is out of a circuit?
-
08-17-2012, 07:10 PM #15
Professional Member*
- Join Date
- Dec 2010
- Location
- Toronto
- Posts
- 1,252
300' on a 1/2" tube is, to me, on the high end of acceptable. Knowing the rest of the info is pretty important.
-
08-17-2012, 07:12 PM #16
Regular Guest
- Join Date
- Jun 2012
- Posts
- 11
I assume it's the circ pump your wanting the specs for? I can email my HVAC guy and ask for the model #.
-
08-17-2012, 07:16 PM #17
Professional Member*
- Join Date
- Dec 2010
- Location
- Toronto
- Posts
- 1,252
Yes, and the total number of loops
-
08-17-2012, 07:28 PM #18
Regular Guest
- Join Date
- Jun 2012
- Posts
- 11
Total loops is 13. I've sent an email off asking for the model of the pump.
-
08-20-2012, 04:42 PM #19
Regular Guest
- Join Date
- Jun 2012
- Posts
- 11
I'm told the pump is a Grundfos UPS26-99FC.
-
08-20-2012, 05:21 PM #20
According to this info:
http://www.us.grundfos.com/web/downl...-UP-SL-027.pdf
That's a three speed pump with a top pumping capacity at zero head of 33 gallons per minute.
So I'm wondering if your pump may not be set at a higher speed?"In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
08-20-2012, 05:32 PM #21
A hydronics tech should be able to purge air from a loop, no DIY.
-
08-20-2012, 05:35 PM #22
Regular Guest
- Join Date
- Jun 2012
- Posts
- 11
Yeah, I'm pretty sure it's at the highest speed. The original installation used a smaller pump but we went to this one to try and increase temps by increasing flow.
-
08-20-2012, 05:55 PM #23
Are the zones that are not working well at the highest point?
-
08-20-2012, 07:51 PM #24
Professional Member*
- Join Date
- Dec 2010
- Location
- Toronto
- Posts
- 1,252
Is the pump feeling HOT, not warm but too hot to keep your hand on for more than 1-2 sec?
-
08-20-2012, 08:48 PM #25
Are any of the tubes getting warm, maybe a few runs are air locked, or pump is bad. There should be temp gauges on supply and return, do u know any temps? 300 feet is too much, 250 is max.
-
08-21-2012, 02:45 AM #26
When you say "get up to temperature," can you explain what that means? Up from where?
One pump? 13x300' loops?
These insufficient zones, in rooms the furthest away from the boiler for those floors?
Boiler make & model? Modern high zoot boiler (to match the house... And if so, why no ECM pump)? Temp setting? Water temp programmable by zone? Reset setting?Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.