Results 1 to 13 of 26
    Jun 2012
    Radiant floor not coming up to temp in two rooms
    Hello,
    We have a new house with radiant floor heating. The heat is provided by an air-to-water heat pump. For the most part the system works well. But we have two rooms that never quite get up to temperature. I can get most rooms hotter than we would want (24C), but these two won't go over 21 even with all the other zone valves closed. I'm suspicious that there's a flow restriction. The HVAC contractor feels that the temperature differentials would be greater that what they are (2C) if there were a restriction. There are no flow meters in the system. The contractor is a good guy but he's run out of ideas. Does anyone have any suggestions as to what we should be looking at?
    Circulator sizing.
    Fort Worth, TX
    Flow test the problematic circuit. Should be a manifold to this zone where a flow test could be done. Whoever designed the system should know how much flow that zone requires.
    Is this house slab on grade or are the radiant tubes beneath wooden subfloors? Could be an insulation issue either way.
    Building Physics Rule #2:
    Building Physics Rule #3:
    Jun 2012
    The downstairs is slab on grade. One of the problem rooms is down there. Upstairs we have tubes set in concrete on top of the subfloor with plank alder finish floor. We've had him confirm the design, I've run the numbers using some online tools I found and we had another contractor run the numbers as well. And realistically, the problem rooms don't have any big differences in heating parameters than rooms right next to them that work fine. So again, I can't help but think it's a flow issue. As far as measuring flow, the manifold is soldered copper pipe with tubing banded directly to it. Putting in flow meters will be a pain. That's why I'd hoped to confirm his notion that low flow could be ruled out by the temperature difference.
    Fort Worth, TX
    The space between the first and second floor (known as an interstitial space in building science terms) in your house...is it sealed and insulated at the band joist, which is where the floor joists meet the top of the first floor walls? If not, you could be losing a good deal of heat in this space due to air movement and conduction.
    Was insulation installed beneath the radiant loops upstairs AND under the slab loops?
    Air in zone piping or thermal envelope issue. Could be kinked line or a number of other issues. Without being on site it is difficult to diagnose. Good luck
    Dec 2010
    Toronto
    What are the loop lengths, number of loops on each floor and the pump model?
    Saint Joseph, MI
    Are there zone vavles to each room? Balancing valves to each zone, or it is one big circuit?
    If you can put a pressure gauge on the supply and return pipe to each zone, you can measure flow by pressure drop.
    Then the question is, how the the heat loss and gain of the different rom compare in relationship to the length of piping... i.e. amount of BTU's being delivered to each room. The colder rooms might simply have less insulation, less solar heat gain or more windows.
    Fort Worth, TX
    I was going to suggest Pete's Plugs (pressure taps) in one of my replies, but then thought about what it would entail to derive any meaningful info from a pressure drop reading, so left that out. IMO one would need to know a lot of info about the loop in question for a PD reading to cross over to a flow rate.
    Therefore I suggested to the OP, as you have, to investigate other potential causes. He did state that with all other zones valved off that performance in the problem zones does not improve. That narrows it down to a few remedies, either increase the temperature setpoint of the entire loop, which uses more energy, increase flow to the problematic zones (which may be limited by loop and pipe size, ensure each loop is completely purged of air, look for ways to slow heat loss from the rooms in question, or check insulation levels beneath each loop.
    Saint Joseph, MI
    Could be as simple as a balance issue. Maybe there aren't balancing valves.
    Fort Worth, TX
    OP said they can throttle down on valves in other zones and the problematic zones do not improve in temperature.
    The first hurdle to clear is to determine if the problem zones are flowing enough water. If they are, the problem may lie in heat going the wrong direction, meaning either into the ground where the slab is, or into the space between floors on the upstairs problematic zone. While a common response to this thought may be "heat rises", the truth is that heat itself goes in all directions. Heated air "rises" due to density variances, but radiant heat moves in all directions. Meaning...if there is not insulation below the radiant loop in the problem zone, or the insulation is inadequate, installed incorrectly, or whatever, heat could be escaping that should rather go into the problematic zone.
    Jun 2012
    There are balance valves although they are all fully open. But in my mind we've ruled this out by the fact that a problem zone doesn't change even when all the other zones are secured.
    Jun 2012
    The loop lengths appear to be around 300'. There are 7 upstairs with three control zones, and 6 downstairs with 5 control zones. I'm currently away from home so I don't have the pump info in front of me. Sorry.
Tags for this Thread