    Quote Originally Posted by Nuclrchiller View Post
    That's a matter of opinion.

    That's a matter of water treatment. With good water treatment, I've heard of units going year without beign brushed.

    Cooling towers in many climates need to be cleaned as often as condenser coils.

  2. #22
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,426
    Post Likes
    I don't understand how the pay back can be the same for both systems. I also, would not bet on the ROI to be 3 years. If they agree to get payed over the the time period they say it will take to get your ROI then they would have a vested interest in making sure they were right. (don't hold your breath) Every time i hear 3 year ROI i double it. I would forecast the next 5 years of water cost and electrical cost. if cost of water, and electrical goes up this would effect the ROI period. Unless you already added in the increases. DO you pay for sewage waste?

    Also, are there any other buildings in your area that has water cooled and are about the same size as yours? If so i would talk with them and get their input. Not sure of the water chemistry but, depending on the type of water you have towers can be the bane of your life.

    Personally i would stay with what you have and make repairs. I would imagine the capital cost comes out of your bottom line. Do repairs come out of common charges? if so why would you dump all that money in a new system? Just wondering, I would think if you took that money and properly invested it, the return would be greater than what you make on the savings over the next three years. -just saying. The ROI will always be there, whether you do it now or later. Unless they are making you a deal you cant refuse.




    anyway not to get to far off track. Overall not knowing all the little details. Unless the entire systems is failing i would make repairs. If you have the money and just want to save money and they really believe they can get you a 3 year ROI, Then that's great, all new equipment today will save money, much has changed over the last 10 years. But again, Who can support for the equipment your will buy. If there is no local support for this new equipment or there are only a few who can work on it, i would shy away.

  3. #23
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    i will be the idiot here!

    what is an MHI chiller?????
    true knowledge exists in knowing that you know nothing.

  4. #24
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by supertek65 View Post
    i will be the idiot here!

    what is an MHI chiller?????
    ok I think it's the panel on the chiller.

  5. #25
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    If I were bidding this, I would look at a third solution. With the amount of runtime they get over there verses our traditional cooling season, payback can occur more quickly. we have less degree days for cooling, I would think by a lot. At any rate, if I had the infrastructure in place for RTAA's, I would look at a repalcement using either screws or turbocore, using evap condensing, with all pumps, evaporater, tower etc, all bundled neatly into one package, and set it in place of those rtaa's. you will see similiar kw/ton performance, and less initial cost, but thats just me. payback would be sooner, with less water treatment involved.

  6. #26
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    but what do I know?

  7. #27
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by supertek65 View Post
    what is an MHI chiller?????
    It's a chiller made by Mitsubishi. The MHI stands for Mitsubishi Heavy Industries.

    @flange I would not consider Turbocor compressors in a desert environment. I think they would not spend much time in their sweet spot and quite frankly the numbers I have seen tell me they suck at full load conditions. There are many very large central plants in Dubai many of which are district cooling facilities.

  8. #28
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    wow!!!!!!
    they have come a long way since the zeros bombed pearl harbor!!!!!!!!!!!!!

    i hope there arent any af those in any army bases!!!!!!!!! LOL





    Quote Originally Posted by KnewYork View Post
    It's a chiller made by Mitsubishi. The MHI stands for Mitsubishi Heavy Industries.
    true knowledge exists in knowing that you know nothing.

  9. #29
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,426
    Post Likes
    Quote Originally Posted by flange View Post
    If I were bidding this, I would look at a third solution. With the amount of runtime they get over there verses our traditional cooling season, payback can occur more quickly. we have less degree days for cooling, I would think by a lot. At any rate, if I had the infrastructure in place for RTAA's, I would look at a repalcement using either screws or turbocore, using evap condensing, with all pumps, evaporater, tower etc, all bundled neatly into one package, and set it in place of those rtaa's. you will see similiar kw/ton performance, and less initial cost, but thats just me. payback would be sooner, with less water treatment involved.
    I like your thinking

  10. #30
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    361
    Post Likes
    Quote Originally Posted by KnewYork View Post
    It's a chiller made by Mitsubishi. The MHI stands for Mitsubishi Heavy Industries.

    @flange I would not consider Turbocor compressors in a desert environment. I think they would not spend much time in their sweet spot and quite frankly the numbers I have seen tell me they suck at full load conditions. There are many very large central plants in Dubai many of which are district cooling facilities.

    Dubai has a design wet bulb of 89 degrees so agree the Turbocor performance would suck, but agree with Flange, given the lack of available wet bulb relief, worth investigating a VSD screw option.


    For information on the Mutsuibishi Centrifugal http://www.mhi.co.jp/en/products/cat...l_chiller.html
    Last edited by Screwit; 08-16-2012 at 08:51 PM. Reason: Can't spell
    Necessity is the mother of invention

  11. #31
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    Didnt know it was that high. Yup, I would be all over me some screws, copeland, bristol, whatever they are called these days. I like those pumps.

  12. #32
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    I'll take tube-brushing over coil-cleaning any day!
    Don't pick the fly crap out of the pepper.

  13. #33
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    obviosuly that is preferred for ease of maintenance, however, thinking slightly outside of the proverbial box, there are reasons why my plan might make some sense. first, it offers a quicker payback than a central plant. second, it doesnt generally require any more footprint or a dedicated mechanical room inside a building, which brings on a whole new set of problems such as refirgerant monitoring, ventilaltion, etc.. it is better than an air cooled solution, and can be designed to run very close to or better than total plant kw for a central plant, depending upon the style of centrifigual chosen.

  14. #34
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    not to mention here in the states, it is a different type of leverage on the building, potentially creating tax saving opportunity over central plant.

  15. #35
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,186
    Post Likes
    Yes, Yes it do suck. Don't recommend it for anyone. The 2nd. to last time I used rods was to get a whole bunch of fill from a tower out of a 1,500 ton absorber bundle. Suck doesn't even start to describe what kind of work that was.

    ...Ron
    Roof Rat

  16. #36
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    One more thing I'm not sure I saw mentioned? How greatly do the loads vary? Centrifugals often have minim capacities around 30-50% load. Screws can run down to 10-15% RLA in many cases. I felt that in many cases, centrifugals were best installed in pairs, on a system with a minimum load, or used as base load chillers together with a screw machine.

  17. #37
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by motoguy128
    Centrifugals often have minim capacities around 30-50% load.
    Centrifugals are capable of turning down to 10% load and if equipped with VSD do so quite nicely. Even w/o VSD they can certainly turn down well below 30%. Can't imagine where you are receiving your information.

  18. #38
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    One more thing I'm not sure I saw mentioned? How greatly do the loads vary? Centrifugals often have minim capacities around 30-50% load. Screws can run down to 10-15% RLA in many cases. I felt that in many cases, centrifugals were best installed in pairs, on a system with a minimum load, or used as base load chillers together with a screw machine.
    What scrrw will run to10/15 % capacity?, thats not even posible with a screw. I think you have your statement backwards.

  19. #39
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Sorry, I'm probably confusing our air cooled unit with 3 compressors that can run down to 10-12% RLA, but that would still be 30% on one compressor.

    I still remember from training I had on Trane centrifugals and rotary that the rotary would go quite a bit lower. Centrifugals seem more "sensitive" and we walked into one out our chillers rooms and it was getting noisy and RLA was only 60% without any apparent issues. But these are lower temp machines. IN another area, a pair of similar centrfugals were running happily at 48-50%. Who knows, maybe the IGV's need looking at on that one. The approach might have been starting to creep up a little too.

    I guess from my limited experience with Trane units, you can run the screws lower loads than the seemly more sensitive centrifugals that find themselves near the edge of surging at times.

    I thought it was something to factor in. A mutili compressor RTAA will defnitely run a much wider range of loads. SO in this case his 456 ton nominal system with two RTAA's could probably run down to almost 5-8% system capacity. A single centrifugal won't even come close and would need a large storage tank to prevent short cycles whe hte building is under low load, at night, during low occupancy periods.

  20. #40
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Don't get % RLA confused with % capacity. There 2 differant things.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •