    Confused replacing the air cooled to centrifugal chiller.

    Dears,

    We are planning to withdraw our 14 year old TRANE RTAA chiller 456 ton capacity (2 No chiller, each 228 ton total 456 ton,unit model RTAA 328) and replace with either same like air cooled chiller or new water cooled centrifugal chiller. We are advised by Mitsubishi to install ETI series 450 ton centrifugal chiller and the water cooled system shall have a power consumption of 0.8 KW against 1.6 KW the existing trane chiller. The additional investment of water cooled system can cover and pay back within 2.3 year by analyzing the local electrical and water cost. I would be interesting your valuable opinions,
    1. Is better to replace same brand air cooled chiller
    2. Comparison the centrifugal chillers of trane vs York vs Mitsubishi vs carrier.

    Regards
    Moideen-dubai

  2. #2
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,427
    Post Likes
    my two cents, factor in chemical treatment and PM maintenance on all equipment to support this. But the pay back on either one is good.

  3. #3
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Water treament will be a major focus. If preventative maintenance is an issue go air cooled. Much easier to clean coils then brush out condenser barrels.

    Sent from my ERIS using Tapatalk 2

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Quote Originally Posted by jdblack View Post
    Much easier to clean coils then brush out condenser barrels.

    Sent from my ERIS using Tapatalk 2
    That's a matter of opinion.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    That's a matter of opinion.
    X2

  6. #6
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    That's a matter of opinion.
    X3

  7. #7
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Cost to go watercooled from aircooled is a big expense... Tower, pumps, building etc. me personally would put in a couple Rtac's and never skip a beat

  8. #8
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes
    moideen- One other thing to think about you could cut down on your maint. cost by using a McQuay WMC. There is no oil and KW/ ton is a lot better then .80, something to think about. -GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  9. #9
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by ga1279 View Post
    One other thing to think about you could cut down on your maint. cost by using a McQuay WMC. There is no oil and KW/ ton is a lot better then .80, something to think about.
    I think he's referring to total system kW. A York YK with VSD will do a whole lot better than .8 kW/ton as well. I think one of the problems with a Turbocor compressor in Dubai is the likelihood that it would run a full load more than it may here in the States. Turbocor compressors don't perform as well at full load as many of their competitors.

  10. #10
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    That's a matter of opinion.
    Okay let me rephrase --- not easier as much as less skilled labor needed

    Hows that

    Sent from my ERIS using Tapatalk 2

  11. #11
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by jdblack View Post
    Okay let me rephrase --- not easier as much as less skilled labor needed


    Hows that

    Sent from my ERIS using Tapatalk 2
    Pokin fun here but it doesnt take a genius to punch tubes.

  12. #12
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by Southern Mech View Post
    Pokin fun here but it doesnt take a genius to punch tubes.
    it is hard to clean tubes wrong...it is very easy to clean a condenser coil wrong and screw the whole thing up...

    what are we up to now? X6?
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  13. #13
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Quote Originally Posted by jayguy View Post
    it is hard to clean tubes wrong...it is very easy to clean a condenser coil wrong and screw the whole thing up...

    what are we up to now? X6?
    You guys just love to argue. Evidently youve never seen someone try to beat a bore brush through a tube and bust it. You think its easy because you have a tube machine and skills. Take a half wit with an adjustable and some rods and brushes and have at it. Good luck

    Sent from my ERIS using Tapatalk 2

  14. #14
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    2.3 years will cover the cost of a tower, piping, pumps, chemicals, etc? Go for it.

  15. #15
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by jdblack View Post
    You guys just love to argue. Evidently youve never seen someone try to beat a bore brush through a tube and bust it. You think its easy because you have a tube machine and skills. Take a half wit with an adjustable and some rods and brushes and have at it. Good luck

    Sent from my ERIS using Tapatalk 2
    straight rods only? that would suck.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  16. #16
    Join Date
    May 2002
    Posts
    949
    Post Likes
    +1 on the centrifugal payback and understand ....

    You WILL HAVE TO maintain all the added equipment and have CONSISTENT and CONTINOUS water treatment being performed at ALL times on both sides , chilled water and condensor .

    as far as punching tubes consider getting a self brushing system that reverses flow every xxx hours and keeps your tubes clean ...which keeps your kw per ton down...

    let your water get trashed and you'll lose your savings in a hurry....it doesn't take years to happen ...i seen tubes fouled in days without proper water treatment ...

    as far as a brand I would go with what is best supported by factory reps / mechanics in your area ...

    On the other hand .....

    That machine goes down you have no cooling ...

    You lose a fan motor on an air cooled you have wiggle room ....

    You have multiple screws and lose one you have wiggle room

    If your going to follow a strict maintenance regimen I would still say centrifugal ...

    If your gonna run it till it quits I would say air cooled

  17. #17
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,427
    Post Likes
    Quote Originally Posted by mikeacman View Post
    +1 on the centrifugal payback and understand ....

    You WILL HAVE TO maintain all the added equipment and have CONSISTENT and CONTINOUS water treatment being performed at ALL times on both sides , chilled water and condensor .

    as far as punching tubes consider getting a self brushing system that reverses flow every xxx hours and keeps your tubes clean ...which keeps your kw per ton down...

    let your water get trashed and you'll lose your savings in a hurry....it doesn't take years to happen ...i seen tubes fouled in days without proper water treatment ...

    as far as a brand I would go with what is best supported by factory reps / mechanics in your area ...

    On the other hand .....

    That machine goes down you have no cooling ...

    You lose a fan motor on an air cooled you have wiggle room ....

    You have multiple screws and lose one you have wiggle room

    If your going to follow a strict maintenance regimen I would still say centrifugal ...

    If your gonna run it till it quits I would say air cooled


    I agree, well said

  18. #18
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    901
    Post Likes
    Thread Starter
    Thanks your replay,
    The chemical treatment and additional centrifugal maintenance cost has also included in the comparison report of air cooled and water cooled system from Mitsubishi. For your reference, please find the attached report from Mitsubishi. But do not include the overhauling charge of compressor. (As per MHI service department recommendation, every 7 year, compressor has to be overhauled) recently we have overhauled 1500 ton capacity MHI compressor, cost is 463531 AED (126182 USD)!!. Now RTAA chiller compressor is failing after 14 years, before it don’t have major maintenance, only replaced some display boards, the authorized Trane service department can remanufacture the compressor by charging 50000AED(13611 USD),but we are the energy save by using water cooled centrifugal.
    Any way we are looking the same proposals from York and trane.

    Thanks
    Moideen-Dubai
    Attached Files Attached Files

  19. #19
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    You might want to consider another manufacturer. I know of one (York) that does not require any scheduled overhaul interval and I have seen many compressors run over 75,000 without ever being opened.

  20. #20
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes
    My apologies to one and all as I jumped the gun with my last post, I did not realize the area we were discussing. Water treatment will be costly as your make-up water will be high and fresh water is costly there to begin with. 14 years of life out in that climate, hell I've seen them in Houston that don't last that long.-GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •