    Hi guys. I just change out a evaporator and a condenser for a w/in ref. I notice the txv outlet is frosting where the spider going to coil. I running R-22 and my pressure is 50psi suction and 260 high side. Site glass is clear and temperature is 40- 38 F. It was running good for a week and the evaporator ice up. I deice coil and everything looks ok except frosting coming out the txv. Is this normal for r-22 ? Thanks Eric
    Jun 2009
    DFW, TX
    Quote Originally Posted by 808jib View Post
    Yes. Has nothing to do with R22. It is normal for anything below 32*f to frost.
    May 2008
    Myrtle Creek. Oregon
    Put a defrost clock on it!
    a stupid question is a question you wont to ask, but don't
    Jul 2012
    Western KY
    Check the box for infiltration. Warm moist air will suck into the box through any opening and freeze on the coil. Check door gaskets and penetrations for line sets and electrical. Also check door closure and latch that they close and hold door sealed. Usually don't need defrost on coolers however if your box is beat up and full of gaps it may be the most cost effective solution as long as it makes set point. Oh ya and tell them not to prop door open.
    Madison, WI/Cape Coral, FL
    Could be low air flow through the cooling coil. This basic. Increase the air flow through the coil.
    Regards TB
    Jun 2010
    Miami
    Wouldn't hurt to check evap superheat. Might need to open up the txv a bit.
    Aug 2012
    I notice some r-22 meduim temp system some sweat coming out the txv and some frost. I know r-12 doesnt frost.
    Aug 2012
    Quote Originally Posted by cboe View Post
    Usually Meduim temp does not require defrost timer since temperature is above 32F.
    Oct 2011
    Chicagoland Area
    In a perfect world.
    California
    Can you explain more about this phenomenon?
    Aug 2012
    Georgia
    Quote Originally Posted by 2sac View Post
    In a perfect world.
    I agree. I service 2 walk in coolers and 2 walk in freezers. Two run r12 and two r22. All have defrost timers. If the cooler was installed charged and left alone it probably would be fine. As soon as you add people into the mix it is over. They can't seem to close the doors! Not to mention plastic and all sorts of other trash that gets on the coil.
    Aug 2012
    How many defrost time you put per day and how long ?
    Jul 2010
    So-Cal
    I usually put it for 15min 3 times during the day and 30-35 min about 2:00am.
    I work for a fast food company that is not open 24hrs they leave around mid night so the 30-35min at that time is ok because no one is opening the door.
    Never iced up again.