manitowoc indigo -full bin problem
Just installed a new machine at a Lonestar. Setup the ice thickness and ran through 1 cycle. the unit finished its harvest and then indicated i had a 'full bin' and that my water curtain was open. neither scenario was true. i reset power on unit and it started back up and did same thing.in setup menu i set binsensor option to 'none' still did the same thing. i then set it to 'bin' and then 'dispenser' which the unit doesnt have anyway. Still did the same thing. i suspect i either have a defective water curtain sensor or the sensor/magnet in door is not activating the sensor. im calling manitowoc in the morning. in the meantime anyone have any other suggestions?
-
02-21-2012, 06:52 PM #2
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Sensor wires connected to board ? Try another magnet ?
-
02-21-2012, 07:34 PM #3
Regular Guest
- Join Date
- Sep 2002
- Posts
- 606
yes wires are connected to board and connected to the right terminals. there is no exposed magnet on these units like the S series. this is an Indigo unit. i dont believe there is a megnet in the water curtain on these units . i believe it is a proximity sensor.
-
02-21-2012, 07:40 PM #4
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Get the model # if you could please.
-
02-21-2012, 07:55 PM #5
might be a dumb question but . . . did you have the curtain off during the cycle for any reason & just not have it back on after it harvested? thus the full bin indication
edit: reread your op u said it wasn't open so i assume it was on .. ohm the bin switch with leads disconnected & see what it reads with curtain open & closed
Sent from my HTC Sensation 4G using Tapatalk
-
02-21-2012, 07:56 PM #6
-
02-21-2012, 09:53 PM #7
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 349
They already have a service bulletin about the ice dampers sticking on certain models and causing a false full bin condition..... If I remember right, you grind down the inside edge of the damper (the damper has the magnet and rotates down to trip the bin switch). If yours has a curtain this may not apply. Check Manitowoc website for applicable service bulletins. Good luck!
-
02-21-2012, 10:22 PM #8
-
02-21-2012, 11:25 PM #9
The switch is easy to test..........Got Ground?
If You Can Dodge A Wrench You Can Dodge A Ball
-
02-22-2012, 10:00 AM #10
Ditto on the Ground. Make sure the machine is grounded properly or those sensors will not work right.
-
02-22-2012, 12:04 PM #11
agree on the ground.
a little off topic but id like to think improper grounding of machines must rank high on calls to the factory for machines that don't function right. . . . for machines in play for a while i bet that high ranking call is filthy machines/components
Sent from my HTC Sensation 4G using Tapatalk
-
02-22-2012, 01:02 PM #12
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
lowtemp,
Do you have a model number for us to work with ?
-
02-24-2012, 07:24 AM #13
Regular Guest
- Join Date
- Sep 2010
- Location
- New England
- Posts
- 41
2things. There is a large washer u need to remove on thickness probe after installation and the is also an adjustable bin control on those units. The settings are in the board. I don't have book in front of me but u should call manitowic and they should set u straight.