    110v between hot line and concrete floor

    I was working on a oil furnace today and was testing the primary control, I has one probe of my meter on th line voltage and the other probe was touching the floor and meter started beeping. I look and it says 115 or whatever so I keep trying and every time the same thing. I guess it's possible but just thought it was wierd.

  2. #2
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,478
    Hot to ground = 120v. Say your standing on concrete with rubber soled shoes. You can grab that hot wire and it wont shock you. Take your shoe off and grab that hot wire. zingg

  3. #3
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,589
    Quote Originally Posted by ar_hvac_man View Post
    Hot to ground = 120v. Say your standing on concrete with rubber soled shoes. You can grab that hot wire and it wont shock you. Take your shoe off and grab that hot wire. zingg
    Ya I get it just surprised me, didn't think I would get 120 to the floor.

  4. #4
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,478
    lol i learned the hard way, working on my washing machine in nothing but boxers

  5. #5
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,589
    Quote Originally Posted by ar_hvac_man View Post
    lol i learned the hard way, working on my washing machine in nothing but boxers
    I guess that's when you know it's time to fix the washer, when all you have left is underwear lol.

  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,804
    Today, system grounds are bonded to piping, structural steel, and rebar embedded in concrete. You are reading 120v because those bonds are connected to the system neutral at the panel. In this case, your concrete is completing a high impedance circuit to your ground rod, and to the neutral at the panel.

  7. #7
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    976
    I guess that's when you know it's time to fix the washer, when all you have left is underwear lol.

    LMFAO...so true so true.....

  8. #8
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,589
    Thanks timebuilder it makes sense now, at the time I didnt think of it like that, I feel dumb now for even mentioning it as I do some electrical work with our sparky sinking ground rods and such.

  9. #9
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by timebuilder View Post
    Today, system grounds are bonded to piping, structural steel, and rebar embedded in concrete. You are reading 120v because those bonds are connected to the system neutral at the panel. In this case, your concrete is completing a high impedance circuit to your ground rod, and to the neutral at the panel.
    That should be low impedance.

  10. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,804
    Quote Originally Posted by second opinion View Post
    That should be low impedance.
    It "should be," but in his case, it is not. HE has a high impedance path between his concrete and the neutral bar in his service panel, probably via the ground under the concrete and out to his grounding electrode, and back to the neutral bar.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  11. #11
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,589
    Quote Originally Posted by timebuilder View Post
    It "should be," but in his case, it is not. HE has a high impedance path between his concrete and the neutral bar in his service panel, probably via the ground under the concrete and out to his grounding electrode, and back to the neutral bar.
    I'm wondering if the fact that the floor was wet (100 year old house leaky basement) it helped the process?

  12. #12
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,224
    concrete also loves humidity and acts like a sponge

  13. #13
    Join Date
    Nov 2008
    Posts
    1,673
    Concrete is a semiconductor and wet concrete is a pretty good conductor. See if you can light a 7-1/2W bulb that's hooked up between the hot line and the floor. If that works, try a 100W bulb.

    Since you're not dead I guess the current flow, 120v through concrete resistance through skin resistance through body resistance and back through skin resistance was less than 20 mA or so. 10 mA is painful and 1 mA is a tingle.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event