Thread: Double float switches
-
08-18-2012, 01:22 PM #27
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,294
I use a float switch that screws into the secondary coil drain... IMO to stop the water BEFORE it overflows the coil pan is the first line of defense.
If the unit is anywhere other than on a concrete floor, it gets a pan float switch also.
The condensate pump ALWAYS goes IN the pan, and the switch in the condensate pump is always wired in.
If the install is an 80% furnace (most are in my area), then I break the Y... If it is a condensing furnace, then I break R.
And I always install a T in the coil drain... it gets flushed each spring.
So far, so good... in 10 years NO sheetrock repairs. NEVER have made a claim on my G/Liab policy... lets see if I get to continue this way.GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
08-18-2012, 08:34 PM #28
Professional Member
- Join Date
- Apr 2008
- Location
- warwick, ny
- Posts
- 39
I want to say thank you to all other techs for your input.I am sorry didnt get back sooner had family issues.I see that two is not a waste. two wet swiches are inportant so you dont have a mess on your hands.That is cheaper than a new ceiling.
Thanks to all.
-
08-20-2012, 02:15 PM #29
Regular Guest
- Join Date
- Nov 2008
- Posts
- 1,656
If half or more of the contractors have claims made at or before the 10 year mark then you are doing better than average, possibly much better than average.
Is there any way to confirm this?
Insurance companies know how many water damage claims per year they get, but they may not want to tell you how many are due to HVAC problems and not due to broken pipes, floods, storms, etc..
-
08-20-2012, 02:32 PM #30
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 572
Nothing said about freeze control?
Seen too many frozen verticals with switches everywhere, sure it'll shut off when enough water gets to a switch. But what do you think happens when that block of ice continues to melt? It's bigger than the primary pan so most of it misses and goes to the emergency pan. Two, three, ten switches won't stop that problem.
Two switches in the same pan? just plain stupid. If it's not stupid why not shoot for ten switches in the same pan.
-
08-20-2012, 03:41 PM #31
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,294
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
08-20-2012, 06:26 PM #32
Regular Guest
- Join Date
- Nov 2008
- Posts
- 1,656
Yes. Is this average or exceptional for contractors like yourself? It sounds good to me but I don't know what to compare it to.
If most contractors go 40 years without a single claim this is not so exceptional, but I don't know. I guess you could survey contractors on this site and ask.
-
08-20-2012, 07:47 PM #33
Professional Member
- Join Date
- Apr 2008
- Location
- warwick, ny
- Posts
- 39
I see everybogys point with the switches. You can't foresee a block of ice if the unit has a problem due to system malfuntion or a era on a homeowner who doesnt do annual maintainance.
-
08-20-2012, 08:39 PM #34
My "This is why you should listen to us & do your yearly maintenance" Speech...
I went to a beautiful house with hand painted murals on the walls & ceiling for a first time maintenance on an 8 year old Spacepak. I quoted a wet switch, new primary pan, and an emergency pan (it didn't have one). The guy said "Naa, it's been fine this long, I just had you guys come out to shut the wife up." The drain primary drain pan was so badly rusted I was afraid to touch it. He paid 10k for the mural & it took the guy almost a year to complete. I told him that it was cheap insurance keep the wife quiet. 3 weeks later I go back on a water leaking call. Half the ceiling was on the floor. Sometimes I told you so just doesn't cut it. (The wife was crying in the bedroom) The guy wouldn't leave so I could take a picture.....
-
08-20-2012, 09:17 PM #35
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,294
It is called taking pride in your work. In my area (and I believe this is true everywhere)... there are contractors who take personal pride in their work; every job is done as if it were their own house or their parents house. Then there are contractors who are only in it for the $$$... and do the least they can get by with. Care to guess which ones have FEW if ANY issues... and which ones have ENDLESS issues? Hint: Statistics have little if anything to do with it.
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
08-20-2012, 09:19 PM #36
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,294
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
08-21-2012, 12:56 AM #37
-
02-08-2013, 03:14 PM #38
Professional Member
- Join Date
- Apr 2008
- Location
- Florida
- Posts
- 238
Condensate Cleanout Code
-
02-08-2013, 09:55 PM #39
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,294
Have not seen that code yet... does not mean it is not there... just I have not seen it yet.
If this is indeed code... then I am thinking a PVC union (Lowes has them, as well some supply houses), in the drain as close to the coil as reasonable. Just open the union and blow it out.GA-HVAC-Tech