08-14-2012, 06:29 AM #14
If the drier is in between liquid line shut off and condenser outlet, when system is pumped down there will be pressure on drier. This would be ok if there was a factory installed schreader inside condenser. You could shut off isolation valves and pump over with recovery machine.
-
08-16-2012, 09:35 PM #15
if its heatpump you can shove the gas into the AH unit if you know what im sayin ....
-
08-16-2012, 09:41 PM #16
Professional Member
- Join Date
- Dec 2009
- Posts
- 22
can you put two biflow driers on a system will it hurt anything
-
08-16-2012, 09:52 PM #17
wont hurt anything , but theres no real benefit either
its only going to act as one big dryer , because inbetween them will never get dirty