    Are Filter/driers required on new installs

    My brother just had a house built and I noticed there is no filter/drier on his ac. It is a brand new install. I brought this up to the general contractor and he told me it is not required on new installs. Assuming (and I know this is a big assumption) the lines were nitrogen purged while brazing and evacuated below 50 microns, this shouldn't be a big deal. However, I seem to recall manufacturers requiring their installation on new units. Couldn't find any requirement in the IMC. Anyone know if there is a code requirement or manufacturer requirement for a Filter/drier.

  2. #2
    Join Date
    Mar 2011
    Posts
    54
    This is what the Ruud installation manual said. They actually provide a filter dryer with the unit- UPQL condensor.

    As an added precaution, a high quality, bi-directional filter drier is recommend- ed to be installed in the liquid line, if not factory installed.

  3. #3
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by dijit View Post
    My brother just had a house built and I noticed there is no filter/drier on his ac. It is a brand new install. I brought this up to the general contractor and he told me it is not required on new installs. Assuming (and I know this is a big assumption) the lines were nitrogen purged while brazing and evacuated below 50 microns, this shouldn't be a big deal. However, I seem to recall manufacturers requiring their installation on new units. Couldn't find any requirement in the IMC. Anyone know if there is a code requirement or manufacturer requirement for a Filter/drier.
    What brand of equipment?

  4. #4
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Look inside the unit to make sure its not there.

    Sent from my ERIS using Tapatalk 2

  5. #5
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    644
    Goodman

  6. #6
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    644
    I will check.

  7. #7
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by dijit View Post
    I will check.
    Factory installed

  8. #8
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    644
    Quote Originally Posted by second opinion View Post
    Factory installed

    In condenser unit?

  9. #9
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by dijit View Post
    In condenser unit?
    Yes

  10. #10
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,084
    His installers pull a vacuum below 50 microns??? Sure! Most RNC installers wouldn't know what a micron gauge is, some around us may not even use a vacuum pump judging from our findings

  11. #11
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    644
    I know, I have seen that too. That's what concerns me. Even saw a guy that had like 5 years of "experience" in commercial that didn't know how to use a vacuum pump. Of course his daddy also worked at the same company.

  12. #12
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,338
    I think all Goodman condensers come with a factory installed drier. I hate this because I don't have the option to pump down to replace. I like to move them outside the condenser after the first recovery.

  13. #13
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by socotech View Post
    I think all Goodman condensers come with a factory installed drier. I hate this because I don't have the option to pump down to replace. I like to move them outside the condenser after the first recovery.
    Why not?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event