    What is the proper way to set a SORIT valve to maintain a walk in cooler @ 35 degrees? Four compressors R507. Evaporator coil 10* TD. Should all compressors be forced on before setting it?

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    I do it like this.

    make sure your suction pressure is bellow your desired SST for the system you're setting. If you have to manual compressors on, do so.

    Then, turn in the SORIT stem to increase the systems SST above design.

    Then, turn out the SORIT stem to unload the systems SST to design.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,677
    Post Likes
    Quote Originally Posted by Phase Loss View Post
    I do it like this.

    make sure your suction pressure is bellow your desired SST for the system you're setting. If you have to manual compressors on, do so.

    Then, turn in the SORIT stem to increase the systems SST above design.

    Then, turn out the SORIT stem to unload the systems SST to design.


    I do this or something similar with ALL pressure regulating valves. Adjust them past their setting, then dial back to it.
    Last edited by jpsmith1cm; 08-13-2012 at 04:34 PM. Reason: clarity



  4. #4
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,524
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post


    I do this or something similar with ALL pressure regulating valves. Adjust them past their setting, then dial back to it.


    Yep it the way I do it has well.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.