08-13-2012, 05:29 PM #27I love the smell of phosgene first thing in the morning:

To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
08-13-2012, 05:41 PM #28
Depends how cold the freezer is, and what temp it is outside. Mild temp day, 230 head, -10 in the box, 16.
-
08-13-2012, 07:33 PM #29
Regular Guest
- Join Date
- Feb 2012
- Posts
- 21
16 PSIG on suction line in good all around conditions? Which would be about -22 on Gauge? So for a SH of 18-20 that means Im looking for a suction line temp of about zero??? Doesn't sound right!!! That would surely freeze up suction line and compressor etc.
SH=Suction line Temp - Evap temp
Or I thoughtLast edited by Lennyb; 08-13-2012 at 07:39 PM. Reason: Adding txt
-
08-13-2012, 07:47 PM #30
You don't work on freezers often, do you?
-
08-13-2012, 08:25 PM #31I love the smell of phosgene first thing in the morning:

To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
08-13-2012, 09:08 PM #32
-
08-13-2012, 09:26 PM #33
If only I could paid extra for those "froze up" calls where the accumulator has ice on it....I could probably afford that nice Caribbean vacation the wife has been wanting for 2 years!
Don't sweat the ice....you're in the home stretch now. sounds like you have the problem narrowed down, seal the deal.
-
08-14-2012, 11:42 AM #34
Professional Member*
- Join Date
- Apr 2001
- Location
- MINN
- Posts
- 932
Is there a stainer on that TEV?
-
08-14-2012, 12:30 PM #35
SH 18-20? Ok don't be offended but you are not looking for the right numbers the right way. SH is the difference between saturated suction temp and actual suction temp and it should be 6-10 at the TXV bulb on a WI freezer. Agin don't be offended I'm not picking just wanna get you goin in the right direction.
-
08-14-2012, 12:35 PM #36
Also don't worry about frosting of the suction line it's going to happen if not insulated because the line temp will be well below 0 on a -10 degree box. The comp will not freeze up if charge and SH are correct.
-
08-15-2012, 11:14 PM #37
Regular Guest
- Join Date
- Feb 2012
- Posts
- 21
No mostly heat pumps and coolers
-
08-15-2012, 11:21 PM #38
Regular Guest
- Join Date
- Feb 2012
- Posts
- 21
So your saying that the Evap line temp at the TXV bulb should be 6-10 for a 404a freezer? Also maybe im just slow but I was under the impression I understood SH
-
08-15-2012, 11:27 PM #39
Regular Guest
- Join Date
- Feb 2012
- Posts
- 21
With R22, 410A, and coolers with 414B, 409A, and 404a. Only 3 freezers on property.