09-01-2012, 09:45 PM #27
1000 volt is usually more than enough...i test ALL motors at 1000 VDC. yes, even 115VAC motors and they do just fine.
Spellin mitsakes bother me.
-
09-02-2012, 10:27 PM #28
-
09-04-2012, 06:26 PM #29
Professional Member
- Join Date
- Jan 2011
- Posts
- 645
Yeah, until you find one that the insulation is compromised. Industry standard for DC test voltages of 120-
Originally Posted by JayGuy
240 VAC motors is 500 VDC. Certainly you can continue juicing those little motors to 1000 VDC until your luck runs out.
The manufacturers of 4160 V motors prefer a continuous application (10 minutes) of approximately 2500 VDC rather than shorter durations of 5000 VDC.
-
09-04-2012, 11:57 PM #30
-
09-05-2012, 12:34 AM #31
Professional Member
- Join Date
- Jan 2011
- Posts
- 645
Like Tom Petty says "you can believe what you want to believe..."
Originally Posted by JayGuy
-
09-05-2012, 07:02 AM #32
Regular Guest
- Join Date
- Jun 2010
- Location
- Miami
- Posts
- 249
There is a reason why there are megger tests....and then they are hi-pot tests.
A megger test is supposed to be non-destructive. Every insulation class has a rating. We are supposed to be protecting investments, not harming them.