walk in rebuild
hey guys, ive got a kold locker by nor lake old walk in 8x8. old r12 system. compressor chatters on start up, not keeping temp (about -5 to 8*). appears to be low charge. i dont want to buy a tank of r12, or really deal with r12 at all. (this is my deer processors walk in). what would i need to replace the condensor, and evap so that it could be run on 404a or a similar refrigerant. model on the box is klf66-cl-26 serial is 91101798 ive never done a rebuild on a box, so i figured i had better ask you guys. thanks. KB
-
08-12-2012, 01:59 PM #2
I've converted a R22 freezer to MO99, replaced the TXV, compressor and the filter driers.
I've also converted a R409a cooler to a R404a, replaced the TXV, compressor, and filter driers.
Also flushed the old line set with the Rx11 flush before putting in the new equipment
Sent from my iPhone using Tapatalk
-
08-12-2012, 02:27 PM #3
Professional Member
- Join Date
- Feb 2004
- Location
- louisville
- Posts
- 46
i guess i worded my request wrong. i need links etc., for whole evaporators, or kits to change this from existing, to a 404a system. cutting out existing txv, is not something that looked like fun. currently its all compression fittings, and none of it is wrapped etc. if possible i would like to replace the entire evaporator with something newer. as i do very little refrigeration, im at a loss of where to shop for what i need.
-
08-12-2012, 02:40 PM #4
-
08-12-2012, 03:30 PM #5
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
-
08-12-2012, 03:47 PM #6
Actually it may help yet.

That Norlake number says it's a 6 x 6, not an 8 x 8.
I suggest doing a load calc and select your own system instead of copying what's there...which is typically undersized in my book.
http://www.heatcraftrpd.com/products....aspx?&fid=959