Results 1 to 13 of 17
    Aug 2011
    Salem Oregon
    Inside a pipe brazed with nitrogen
    Just a cool Pi I took on an install six months ago. It's a 2 1/8 return line on a Leibert XD system. They tell you in class that you flow Nitrogen to prevent oxidation on the inside of the pipe but it's pretty cool to see it for yourself. The picture shows a 10 foot length of pipe and a brazed 45.
    Feb 2011
    Orange County, in a Galaxy far far away...
    This is exactly the reason why I use a flowmeter, 3 psi is all it takes for a couple of minutes and it'll save a call back later when drier's plugged or worse...
    You cannot cheat an honest man. But that doesn't stop people trying!
    Jan 2011
    Boston, MA
    Sweet pic for sure!
    I'd like to see the same shot but without nitrogen being purged through.
    Probably be a cool side by side comparison to show non believers.
    Calgary, Alberta
    Without nitrogen it looks the same as the outside of the pipe. In school my teacher had us do all types of brazing and soldering then cut our joints down the middle to check penetration and heat control. You could tell who used nitrogen and who didn't.
    Aug 2011
    Salem Oregon
    Quote Originally Posted by FrostyBeer View Post
    Not possible at the time. No room in the schedule for doing work twice. Not to mention the price of a wasted fitting. $$$
    Jan 2011
    Boston, MA
    I mean like on some scrap in some spare time
    Aug 2011
    Salem Oregon
    good point
    Sweet pic for sure!
    Jan 2011
    Boston, MA
    Quote Originally Posted by stopro1 View Post
    Nice!! Did you take that pic?
    Aug 2012
    MA
    Awesome pic man... I remember learning about this is school, must admit I have never done it... ;/
    Apr 2005
    nyc
    The flow rate for pruging with nitrogen is 3-5 CFH----That's cubic feet per hour-----which is not alot of nitrogen. I usually go 10CFH.
    Aug 2011
    Salem Oregon
    How do you measure/calculate the CFH you are using? Is it the same flow rate for different pipe sizes?
    I always just put 2 or 4 psi on the gauge. That puts more CFH in a larger pipe than a smaller one.
    Apr 2005
    nyc
    Quote Originally Posted by Eric S View Post
    Flow meters can be purchased at any welding supply house........you'll save a ton of money on nitrogen. As far as the flow rate for different size pipes, I would assume the larger the pipe the more flow you would need. The correct procedure is to put an oxygen sensor at the end of the pipe and when you 0% oxygen you start brazing. Oxygen sensors can be quite expensive though.