  1. #14
    Join Date
    Feb 2012
    Location
    Toronto Canada
    Posts
    1,003
    Quote Originally Posted by kirbinster View Post
    They are coming out tomorrow, between 8am and noon. I had them put a gauge on it when they did the fan and they said it was fine, but it had only been running about one minute at the time.
    He wasn't one of those super cool Techs that hook up the Blue gauge and see 40 and everything is allright was he? Cause he should have hooked up 2 gauges one red to read highside one Blue to Read lowside. Sounds like High head if she is still charged to me.

  2. #15
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    391
    You nailed it, he only hooked up one gauge which I thought was odd - but I did not take note of which one it was.

  3. #16
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    1,626
    did he have a bottle of gas hooked up to the gauges? if so, it was just the blue gauge he connected... and it's useless for determining issues with pressure in the condenser...
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman

  4. #17
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    2,094
    Its very possible that the fan has got nothing at all to do with the problem & there is another problem now. There are quite a few things that can cause a pressure switch to trip but given the info you've posted & of all the possibilities my guess is that the fan is running backwards. I'd say that's about a 25% probability so i wouldn't bet any money on it.<g>
    Gary
    -----------
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.

  5. #18
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,201
    Quote Originally Posted by garyed View Post
    Its very possible that the fan has got nothing at all to do with the problem & there is another problem now. There are quite a few things that can cause a pressure switch to trip but given the info you've posted & of all the possibilities my guess is that the fan is running backwards. I'd say that's about a 25% probability so i wouldn't bet any money on it.<g>
    There's an idea..Kirbinster, can you put a pice of paper on top of the fan? Does it blow it away or pull it in?
    Every customer you take for granted today will be someone else's tomorrow.

  6. #19
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    391
    No refrigerant hooked up, he just connected one gauge.

    The fan is running the correct way, as I had a long discussion with him about which way it should run. It is sucking are through the coils and venting it up the top of the unit.

  7. #20
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    1,626
    try the paper test anyway. if its blowing out the top of the coil, and sucking in from the grille it could still be fan placement causing an issue.
    get a small piece of paper. start at the bottom of the coil, and lift slowly towards the top. if it sucks in at the bottom, but towards the top it blows out, you have at least found a problem. if it sucks in on the grille towards the outside or the inside, it points to other problems as well.
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman

  8. #21
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    10,449
    You said the coils are clean. Does that mean someone actually CLEANED them, or are they merely getting the eyeball pass of "clean"?
    "In this house we obey the laws of thermodynamics!"

    - Homer Simpson

  9. #22
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    391
    Quote Originally Posted by Shophound View Post
    You said the coils are clean. Does that mean someone actually CLEANED them, or are they merely getting the eyeball pass of "clean"?
    Purely an eyeball examination. I can see through the fins and there are no globs of stuff on them. Again, everything was fine till a week ago when the shaft on the fan broke.

  10. #23
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,294
    One gauge ? What a lazy.......well you know what

    It's unfortunate that you had to deal with someone that had a terrible work ethic.

    I would ask for another tech. How could he leave with the unit tripping or did he not test it ?

    So one gauge and then doesn't actually test or wash the coils ?

    Useless.

  11. #24
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    391
    Well I think the only reason he put one gauge on the unit was because I asked him to test the refrigerant level, he was not even planning on doing that. He did sort of test the unit, he turned it on and it ran for a few minutes. The problem is that it does run for a few minutes, it takes 15 to 20 minutes for it to trip. In all fairness to him, I don't think too many people would have waited around for 20 minutes - but maybe I am wrong.

  12. #25
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    10,449
    Could be wrong motor and blade combo. Could be capacitor was not changed when new motor was installed. Visual check of coils not good enough...clean them and then there is no doubt. Only a low side gauge? Don't even bother calling that moron back out. Hire a comptetent technician.
    "In this house we obey the laws of thermodynamics!"

    - Homer Simpson

  13. #26
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,467
    Condenser is ALWAYS dirty, even if its shiny. Lazy bas!@#$ dont want to drag their water hose out. Still, the problem occurred after the motor and blade change so thats where I would focus and yes, Id wait 20 minutes or an hour if I had to.