    What to do to fix cooling unit not starting up but fan blowing on YORK HVAC?

    Problem: HVAC cooling blowing but not cooling.

    Situation:
    I have a York Diamond 90 heating/ac unit for the top two floors of our town home (matched unit for bottom two floors, which works fine). The unit is 11 years old and has been serviced before each heating and cooling season.

    About 4-5 years ago we experienced the cooling on the unit would not start up, but the fan would run. Typically the indoor unit would freeze up. The first thing the technician did was add freon. Later the company had us replace the outside compressor. Then a year or so later the problem started again, almost always thetedhnician added freon and it worked, for months. Every summer when really hot outside the same problem would occur, they would add freon and it would again for awhile.

    Only think that works, for awhile: if I turn off the switch to blower, the blower shuts off. I let sit for a few minute. Then turn back on and the unit resets and starts to blow cool air ... For about an hour or so ... Then cooling stops and just blows hot air -- until I flip switch again, which I assume resets something.

    What we've tried in last month:
    1. Had outdoor compressor cleaned -- dramatically improved the strength of the air blowing from the fan
    2. Had more freon added -- tested line temp at outdoor unit is something like 56 degrees
    3. Change thermostat -- no help
    4. Replaced circuit board -- helped for while
    5. Wrapped the TXV valve -- no help.
    6. Replaced air filter -- no change

    What do we need to try next to solve the problem?

    Thanks in advance for the help.

  2. #2
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,627
    Get a better technician, one that will find where the refrigerant is going

  3. #3
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,629
    The first step is to have the company find where the refrigerant leak is. From there you can decide if cost of repairs vs system replacement is the best move.

  4. #4
    Join Date
    Aug 2012
    Posts
    15
    Thanks, but why do you think it resets and works when I turn the indoor switch off, then on?

  5. #5
    Join Date
    Jul 2005
    Posts
    5,510
    Quote Originally Posted by AlKoch View Post
    Thanks, but why do you think it resets and works when I turn the indoor switch off, then on?
    The fault triggers the board to shut down the unit. It's a safety feature. Resetting the board is a bad idea when the fault hasn't been found and corrected first, since it will occur again. Allowing the system to run, even breifly, while a fault condition exists could lead to additional component failures, even to the failure of the safety switch that is locking the board out.

  6. #6
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,629
    There are safeties built into better quality units to protect the equipment. You're resetting those safeties by turning the power off.

  7. #7
    Join Date
    Aug 2012
    Posts
    15
    Quote Originally Posted by martyinlincoln View Post
    There are safeties built into better quality units to protect the equipment. You're resetting those safeties by turning the power off.
    Thats really helpful, so the problem is occurring elsewhere. Given what we've already tested for and tried what other areas should we test for or try?

  8. #8
    Join Date
    Jul 2005
    Posts
    5,510
    Quote Originally Posted by AlKoch View Post
    Thats really helpful, so the problem is occurring elsewhere. Given what we've already tested for and tried what other areas should we test for or try?
    If you read the rules for this forum, then you know that DIY questions aren't allowed.

  9. #9
    Join Date
    Aug 2012
    Posts
    15
    Wasn't DIY question -- there is no way I am capable of doing myself. I was simply trying to understand where to have technician look when now when he comes back tomorrow. Any ideas?

  10. #10
    Join Date
    Jul 2005
    Posts
    5,510
    Quote Originally Posted by AlKoch View Post
    Wasn't DIY question -- there is no way I am capable of doing myself. I was simply trying to understand where to have technician look when now when he comes back tomorrow. Any ideas?
    Same thing. The people reading would see the info either way, so it doesn't matter what your intentions are.

  11. #11
    Join Date
    Aug 2012
    Posts
    15
    Uumm, no need for personal attacks on how "smart" someone is whe you don't even know them.

    And I did trade my original company / technician in for a new one -- late last week. The first tech with my maintenance company, who appeared to be a newbie, said "need to buy whole new system" and gave me number of his sales guy.

    The new tech came last week and is coming again tomorrow, after testing, trying a few things (at midnight) and scheduling to come back again after researching. I'm simply trying to understand the problem and potential solutions so I can be better informed.

  12. #12
    Join Date
    Jul 2005
    Posts
    5,510
    Quote Originally Posted by AlKoch View Post
    Uumm, no need for personal attacks on how "smart" someone is whe you don't even know them.

    And I did trade my original company / technician in for a new one -- late last week. The first tech with my maintenance company, who appeared to be a newbie, said "need to buy whole new system" and gave me number of his sales guy.

    The new tech came last week and is coming again tomorrow, after testing, trying a few things (at midnight) and scheduling to come back again after researching. I'm simply trying to understand the problem and potential solutions so I can be better informed.
    I figured that you'd misread my reply, so I immediatley altered it.

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,563
    Quote Originally Posted by AlKoch View Post
    Wasn't DIY question -- there is no way I am capable of doing myself. I was simply trying to understand where to have technician look when now when he comes back tomorrow. Any ideas?
    If the new company is already trying to sell you a new unit, that doesn't inspire a tremendous amount of confidence.

    Maybe have a look at our Contractor locator map.

Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event