Does the unit have a TXV or a fixed metering device? What method was used for charging?
The Day You Think You Know Everything Is The Day You Stop Learning.
The AC (3 tons) in the home (about 1600 sq ft) I am renting was replaced less than a month ago.
Thermostat setting: cool to 78 deg F.
Average outdoor temps: Day 105 deg F; Night 82 deg F
Observations:
1) Temperature never goes below 81 deg F, even at night.
2) Air coming out of the vents does not feel cool.
3) High pressure line both near the indoor evaporator & the outside condenser do not feel warm.
4) Low Pressure line both near the indoor evaporator & the outside condenser feels cool (but not as cool as the ones my neighbors' home ACs).
5) Low pressure line both near the indoor evaporator & the outside condenser do not sweat.
6) Unit just keeps running but since the target temperature is never reached, the unit never stops.
What the AC technicians said:
1) Thermostat was not set properly.
Action Taken: I had the technician set the thermostat himself just to make sure.
Result: No change in AC cooling performance
2) The filters need to be changed.'
Action Taken: Put in new (regular) filters both at the evaporator & at the door leading to the space where the evaporator is hidden.
Result: No change in AC cooling performance
3) The temperature outside is too hot that the AC can't keep up.
Action Taken: Added insulation to the doors and windows where warm outside air was probably passing through.
Result: No change in AC cooling performance
4) Freon not enough
Action Taken: AC tech took measurements at the condenser & said that the freon levels were OK.
Result: None since the property manager did not want to add freon if levels were OK.
The property manager says that since the AC techs already checked the system twice after the new unit was installed and did not find anything wrong with it, she can't do anything else for me.
That is unacceptable since my neighbors' ACs are the same as ours and whose houses are of the same size and yet their homes are cool, even during the hot afternoons.
Mine does not even go below 81 at night.
I wake up in the morning before the sun rises and I'm lucky if the temperature gets to 81 deg F.
I suspect that either the AC unit was improperly installed, that they failed to do something, or something was improperly done.
I think I'll be better off opening the windows and turning on the ceiling fans.
I would like to know what other things need to be considered based on the observations I made and what else need to be checked.
It's really uncomfortable at home, especially during the mid to late afternoons when the indoor temp goes up to 90 deg F (in spite of a thermostat setting of cool 80 deg F).
My electric bill is almost double of what I normally get... I expect the next one to be higher.
On top of that, I have a 14-moth old baby at home.
Please help!
Does the unit have a TXV or a fixed metering device? What method was used for charging?
The Day You Think You Know Everything Is The Day You Stop Learning.
Move to a house that the ac works properly ,your land lord probably had low bidder do the job
is this cooling only or heat pump; or did I miss that info?
It`s better to be silent and thought the fool; than speak and remove all doubt.
many signs of what you are reporting point to the problem. unfortunately, we would have to be there to fix the problem.
you have two choices. call a qualified service tech out, and pay them to fix the system, or move. if you pay to fix it, it's POSSIBLE the landlord will reimburse you for the repairs, but unlikely.
The TRUE highest cost system is the system not installed properly...
Find a HVAC-Talk Contractor by clicking here
Click below to BECOME a pro member
https://hvac-talk.com/vbb/forumdispl...ip-Information
Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?
I am yourmrfixit
I don't believe there is a TXV.
All I was told is that after replacing the condenser unit outside they checked the freon levels and said they were OK.
Post brand and model number of both the inside unit and the outdoor unit.
AC Condenser unit was replaced about 3 week ago.
Specs:
Goodman GSC130361GA
208 - 230 volts AC
60 Hz
Fan motor: 1.10 FLA; 1/6 HP
Compressor: 13.4 RLA; 74 LRA
Min Ckt amps: 17.9
Nominal operating charge: 77 oz (R-22)
AC Evaporator coils were acid washed a week before the condenser was replaced.
Specs:
Payne model PF1MNC036
Prod Num: PF1MNC036000AAAA
208 - 230 volts AC
Motor: 2.4 FLA; 1/3 HP
Phase 1
60 Hz
R-22 design PSIG: 300
outdoor unit is an A/C only unit, R22 dry ship. Indoor may have strip heaters if your in an area that needs heat once in a while.
They may not have the proper metering device in the indoor unit.
Got a nice little mismatch here but being straight cool, probably not bad enough to affect performance that much. Efficiency could be compromised a bit. Were you in there with the old system? Was it a Payne A/C that matched the air handler? Any idea what kind of failure the old outdoor unit had?
I was here before the old system was replaced but, unfortunately, I was not able to note the specs of the system that was replaced.
All I know is that the fins of the condenser unit was at least 50% damaged when it was pelted by hail last March.
I have a pix of the old condenser.
Note that the front and the left side have the same damage since that was the direction the hail was coming from.
Does that look like cosmetic damage.
At least that's how one of the AC techs described it to the property manager which she actually believed even when I showed it to her.
with tag info posted, looks like an air handler and it shows TXV as metering device.
evap, if read correctly, appears to be a size match to cond unit- 3 ton.
you definitely have an issue, but without being there and the info you posted, we can only offer educated WAGs; incorrect refrig, incorrect fan speed, improper operation of TXV, leaking duct work, etc.