-
a problem unit
hello fellow techs i have a a/c system that has stumped me and would like to see what everyone else thinks. call: not cooling good in afternoon.
I have a 4 year old 4 ton trane 16seer 410-a heat pump that in the afternoon does not satisfy and has a 4 to 5 degree differance in set point, i have called trane and still awaiting a prognosis. this is my second day on this call so here are the details.
my first arrival 3:00pm (first day)
my pressures @ 143/463psig
40sh-6sc
ambient temp 104'F
delta t 19'F return temp 86'F supply temp 67'F
wet bulb 78.3
system shows symptoms of low charge due to high superheat and low subcool readings. condensor coil clean washed several times to make sure. decide to return in the morning to see what changes.
8:30am (second day) system maintaining
my pressures 121/344psig
35sh-5sc
ambient temp 93'F
delta t 19'F return temp 77'F supply temp 58'F
compressor amp draw 13.5 fan motor amp draw 0.9 fan is on high speed.
i decide to charge the system to get 10'F sc and drop my superheat and raise my subcooling at this point my main concern is my head pressure. i decide to return in the afternoon again to see my changes
3:00pm (second day)
my pressures are fluxuating between
154/520 and 149/500psig
my subcooling and superhead are also doing the same (but much better)
11-14'F sc - 13-16'F sh
ambient 104'F
discharge temp from motor 136'F
compressor amp draw 20.5 fan motor 1.0
the system is cooling a little better as you can tell from the superheat and subcool readings, but the head pressure is thru the roof and now my compressor is over amping. i thought maybe reversing valve could be leaking but common suction and suction is same only 5'F difference between c suction and @ evaporator. i dont believe it is the txv due to being able to maintain sh and sc plus when removing the bulb valve opens. also ajusted indoor motor and checked duct work (duck work is a issue but i dont believe it is THE issue) any advise would be much appreciated, oh and system is in cooling second stage
-
Those are some crazy head pressures. Have you considered non-combustibles in the system? Also, it may stupid but have you checked to make sure the valves are comepletely open?
Good luck
-
You mentioned duct issue. Never underestimate the ducts. Is the handler in the attic? Pulling attic air through the return?
-
blocked dryer, check temp drop across dryer, txv?? dont sound like it but if I were to open that system dryer, txv, new freon, I bet your good to go clean the coil too! How old is it, sounds like the motor outside could be getting hot and slowing down, possible yes likely no. If you do have a problem , well we see you do duh, it might be overcharged now, maybe the screen before the txv is partially restricted, still doesnt explain the low subcool though, check fan op and cap very good
-
i thought that to maybe it being non-combustables but my superheat and subcool are regulated too well in my opinion to be non-combustables. the issue also happened all the sudden too... not stupid at all i checked both txv valves the outdoor tvx has a bypass which there is no temp rise or drop. and the indoor txv will open by removing the bulb but my head pressure is insane
-
You might check the TXV versus the Trane recall. I had a similar situation where the TXV was not opening completely. The fact you have a bouncing head pressure would lead me to believe your TXV is acting up.
-
 Originally Posted by hvacmike85
blocked dryer, check temp drop across dryer, txv?? dont sound like it but if I were to open that system dryer, txv, new freon, I bet your good to go clean the coil too! How old is it, sounds like the motor outside could be getting hot and slowing down, possible yes likely no
checked the dryer is not clogged, checked fan motor okay during all of this running like a camp lol 4 years old
-
 Originally Posted by Pete954
You mentioned duct issue. Never underestimate the ducts. Is the handler in the attic? Pulling attic air through the return?
that is a issue a big issue but according to the customer it was fine a week ago.. try telling him he needs new duct work, the unit has wall chases i have a 6 degree difference from vent to plenum
-
Did you clean the condenser coil? Also possible Infiltration of hot air into the return air duct? Make sure airhandler fan on high speed..
Living the dream !!
-
 Originally Posted by d.crowder
checked the dryer is not clogged, checked fan motor okay during all of this running like a camp lol 4 years old
well with it being under warranty, thats good at least, verify airflow of course, I'd change txv, dryer, change whatever could even be possibly wrong, your time is too valueble to go back 4-5 times, do it while its down, not that I've had to do that much, but there's been a few that I didnt know what part fixed it, but I knew it was fixed
-
Where were you taking your temp reading to determine the superheat?? At the TXV bulb or at the condenser? How long is the line set, does it go through a crawlspace or attic??
-
condensor coil clean as a whistle, no airflow restrictions what so ever, i changed the speeds on my indoor motor several time to see any change.. none that would make a huge difference... i have a idea but just a idea the 16 seer trane compressor has a bridge rectifier that opens and closes a little between first and second stage (one compressor) but im not quite sure how to check that. im still waiting on a call from trane talk to them once and he told me he'd call back...not a good sign
-
 Originally Posted by Toddbrewster
Where were you taking your temp reading to determine the superheat?? At the TXV bulb or at the condenser? How long is the line set, does it go through a crawlspace or attic??
line set only 25 feet not long at all i took readings everywhere lol, common suction, after reversing valve and suction in at airhandler. for my subcooling before and after dryer in unit and outside of unit
Posting Permissions
- You may not post new threads
- You may not post replies
- You may not post attachments
- You may not edit your posts
-
Forum Rules
|
Related Forums
The place where Electrical professionals meet.
|