08-12-2012, 11:24 AM #14Can someone please explain to me -
Why is there never enough time to do it right the first time, but plenty of time to do it twice?
Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241
Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113
Find your local HVAC-Talk Contractor: http://icemeister.net/aop_map.html
-
08-12-2012, 01:53 PM #15
No, it would be energized and de-energized by calls to Y to the outdoor unit, so it will close when the system cycles off, and open when the system cycles on.
It simply stops the flow of refrigerant when the compressor stops running, no pump down.
There is no consideration needed, other than making sure the LL solenoid is a bi-flow type.
In a long line set application, with the majority of the liquid line above the condenser, the LL solenoid should be installed within a couple of feet of the outdoor unit.
In addition to reducing refrigerant migration to the low side, it prevents the refrigerant in the liquid line from draining back to, and filling the condenser coil.
When the condenser is filled with liquid there can be some really nasty spikes in discharge pressure, and extreme vibration and compressor noise when a compressor starts up, especially with scroll compressors.If more government is the answer, then it's a really stupid question.
-
08-12-2012, 02:23 PM #16
Now that makes TOTAL sense. That is exactly what I was thinking, for some reason just could not get it formulated into words.
Thanks Mark, at least I know I was going in the right direction.Can someone please explain to me -
Why is there never enough time to do it right the first time, but plenty of time to do it twice?
Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241
Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113
Find your local HVAC-Talk Contractor: http://icemeister.net/aop_map.html
-
08-12-2012, 07:30 PM #17
Bi directional solenoid valve would do the trick.
And no need for a p-trap if the evaporator is HIGHER than the condensing unit.
And compressor was "trying to slug liquid"....what on earth does that mean???
-
08-12-2012, 10:37 PM #18Can someone please explain to me -
Why is there never enough time to do it right the first time, but plenty of time to do it twice?
Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241
Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113
Find your local HVAC-Talk Contractor: http://icemeister.net/aop_map.html
-
08-12-2012, 10:46 PM #19
Cool thanks guys (especially Mark Beiser) for the information and explanations. I will throw a LL solenoid in tomorrow. One last quick question, I am going to pump the system down and I'm wondering how many pounds of refrigerant you can jam into a 5 ton compressor. The reason I ask is because I added several pounds to the system to get the charge dialed in, the factory charge is about 15 if my memory serves me. Are these things built to hold 18-20 pounds of refrigerant in a pump down? Also, I'm not 100% sure how much is in the system, I think there was a loss of charge somewhere while it sat in the warehouse for years. I did not hear a refrigerant rush when I cracked the valves and it was way undercharged after adding refrigerant for the lineset length.
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
08-13-2012, 02:11 AM #20
Since it is a heat pump, make sure you get a bi-flow LL solenoid.
With your lineset length, you won't be able to pump the entire charge down, as there is more refrigerant in the system than can be stored in the condenser.
Use the system to push some out into a recovery cylinder, then pump the system down.
Also, if the system does not have a TXV at the indoor coil, I'd highly recommend installing one, preferably a non bleed type.
A non bleed TXV will help prevent migration to the low side, as well as increase cyclical efficiency in the cooling mode.
LL solenoid at the outdoor unit prevents liquid migration/drain back to the outdoor coil.
Crankcase heater prevents migration to the compressor.
Inverted trap at the indoor coil prevents liquid refrigerant, that condenses in the indoor coil, from running out all at once and slugging the compressor when it starts.
These are the things that will help a system with long lines live a long and happy life.If more government is the answer, then it's a really stupid question.
-
08-16-2012, 11:59 PM #21
So now the system has a crankcase heater, TXV, inverted trap, and a bi-flow LL solenoid. The solenoid made a big difference, its no longer making that godaweful sound after sitting for a few hours and starting up. Thanks again for the help!
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
08-17-2012, 12:12 AM #22
Cool. Glad how everything turned out. Isn't it amzing how things work when they are properly installed?
-
08-17-2012, 08:17 AM #23
Your brain is stuck in Commercial Refrigeration mode .... come back to Residential

In comm refrig , yes LLS pumps the unit down and shuts off with assistance of LPS , but when used in Resi , LLS is generally used as a road block to keep things where they need to stay , and is energized same time as contactor. Its all shut down at once.
-
08-17-2012, 08:23 AM #24
-
08-17-2012, 09:28 AM #25
Professional Member*
- Join Date
- Aug 2008
- Location
- Burlington , Mass
- Posts
- 442
I agree with a liquid line solenoid. Not pumping the unit down, just closing when the call is satisfied. Install it in the liquid line close to the evaporator. That will keep liquid from migrating on the off cycle.
I'll be there when I get there and not a minute later
-
08-17-2012, 05:01 PM #26
I've seen them at the indoor coil and at the OD unit .... i guess it doesnt really matter
Both should have a yellow wire close by ...



Reply With Quote