    R134a TXV bellow gas with R12 system charge big deal?

    CFC12
    SST: 40-50F
    SCT: 125 - 180F
    TXV SH delta 5-8F
    The compressor is a variable capacity type with constant target suction pressure.

    I'd like to get some input on drop-in installation of R134a bellow TXV into a R12 system.
    The vapor pressure difference between HFC134a and CFC12 in the evaporator temperature range given above will cause TXV to respond as if sensing bulb is 2F cooler than it really is compared to a matching bellow charge & system charge pair.

    This MVAC TXV has an adjustment screw at the liquid line entry but to tweak it, the system has to be opened. Since getting it adjusted right on first try isn't guaranteed, so this would be just as, if not more time consuming than replacing the bellow charge with R12.

    Anyways, uncompensated, my speculation is that R134a TXV would cause the SH to increase from 5-8 to 7-10(as measured at evaporator outlet, not compressor).

    If my speculation is right how much relative capacity loss can it be expected?

  2. #2
    Join Date
    May 2003
    Location
    Utah
    Posts
    819
    Post Likes
    Two things to consider when applying TEVs:

    1 - Capacity, which is based on the TEV port size & stroke, the thermodynamic properties of the refrigerant, and the conditions of the application. A TEV that is selected for R-12 will have approximately 20% more capacity when using R-134A...this due to the thermodynamic properties of R-134A.

    2 - What thermostatic charge will provide the proper bulb pressure (applied to the top of the TEV diaphragm) to counteract the evaporator + spring pressure (applied to the bottom of the TEV diaphragm) such that the valve can maintain an operational superheat.

    The characteristics of the R-12 thermostatic charge are close enough to what is required for R-134A to operate properly. In fact, a valve manufactured for R-134A is simply an R-12 valve, with the capacity rating adjusted for the new refrigerant. The factory R-12 thermostatic charge is identical to the factory R-134A charge.

  3. #3
    Join Date
    Jun 2011
    Location
    New Braunfels, TX
    Posts
    113
    Post Likes

    Converting back

    Quote Originally Posted by bunny View Post
    Two things to consider when applying TEVs:

    1 - Capacity, which is based on the TEV port size & stroke, the thermodynamic properties of the refrigerant, and the conditions of the application. A TEV that is selected for R-12 will have approximately 20% more capacity when using R-134A...this due to the thermodynamic properties of R-134A.

    2 - What thermostatic charge will provide the proper bulb pressure (applied to the top of the TEV diaphragm) to counteract the evaporator + spring pressure (applied to the bottom of the TEV diaphragm) such that the valve can maintain an operational superheat.

    The characteristics of the R-12 thermostatic charge are close enough to what is required for R-134A to operate properly. In fact, a valve manufactured for R-134A is simply an R-12 valve, with the capacity rating adjusted for the new refrigerant. The factory R-12 thermostatic charge is identical to the factory R-134A charge.
    I have a 2015 Ford Transit that is massively under capacity for cooling. Obviously it was designed for R-134a, but I was wondering if it were possible to "go back" (never was) to R-12 to gain some additional capacity. Pump down, drain Oil, convert to POE and charge with R-12?

  4. #4
    Join Date
    Feb 2016
    Location
    Florida
    Posts
    482
    Post Likes
    It's doubtful, maybe another issue with the system. Is your cab isolated from the rest of the van?

  5. #5
    Join Date
    Sep 2006
    Posts
    67
    Post Likes
    R12 and Poe not good. You might get better cooling by charging with R414, company claims abt 20% gain,also works with Poe, or mineral oil. Just saying.

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,516
    Post Likes
    On really hot days , always try to park in the shade , even if you need to walk 50 yards

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,073
    Post Likes
    Quote Originally Posted by oldfart View Post
    R12 and Poe not good. You might get better cooling by charging with R414, company claims abt 20% gain,also works with Poe, or mineral oil. Just saying.
    Why?