    I recently installed a Mitsubishi MUH-09TW. This unit was not being used in one location and moved to another building. Prior to be moved there were no issues.

    In the new location I mounted the condensing unit on brackets and ran the lines straight out through the wall. The lineset turned out being only about 3' long. I've read the specs on this unit and it doesn't mention anything about removing charge for a short lineset (total charge 2 lb 3 oz).

    The unit's small (liquid?) line is frosting up from the king valve to a couple of coils in the evaporator. Supply air today was 71 degrees, outside temp is 82 dewpoint 72.

    It doesn't seem to be cooling properly but short of reclaiming and recharging I'm not sure which direction to go.

  2. #2
    Join Date
    Jun 2008
    Posts
    36
    Post Likes
    Thread Starter
    delete post please

  3. #3
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,679
    Post Likes
    I would have a service tech recover the refrigerant pressure test the system pull a vacuum to at lest 300 microns and weight in a new charge