    2 ton higher amps than 2.5 ton?

    Why does a 2 ton condenser have more amps than a 2.5 ton?

    Name:  amps.jpg
Views: 179
Size:  63.3 KB

  2. #2
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    155
    Could be a misprint, but it is carried over to circuit ampacity as well.

    Perhaps they are using the same compressor in both and as the compressor will see a smaller condensing coil it might also see a higher head and running amperage at the same conditions?

  3. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,390
    Or, a model compressor that draws more amps. Could be due to model or manufacturer.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  4. #4
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,222
    It's Rheem, and the discrepancy seems to be consistent across much of their line.
    Coils have the same face area.
    There is 200 more CFM on the 2.5 ton unit.
    The locked rotor amps are higher for the 2.5 ton unit.
    The 2.5ton requires a 25A fuse/circuit breaker. 25A breakers are an oddball size for many panels, I can't remember seeing any.
    The EER/SEER ratings are similar for both units, which makes me think the 2 ton would have to use less power since it has less output.

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,164
    probly has different run cap mfd

    30 , 35