    Jun 2001
    2 ton higher amps than 2.5 ton?
    Why does a 2 ton condenser have more amps than a 2.5 ton?
    Jun 2012
    Northern NV
    Could be a misprint, but it is carried over to circuit ampacity as well.
    Perhaps they are using the same compressor in both and as the compressor will see a smaller condensing coil it might also see a higher head and running amperage at the same conditions?
    Southeastern Pa
    Or, a model compressor that draws more amps. Could be due to model or manufacturer.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jun 2001
    It's Rheem, and the discrepancy seems to be consistent across much of their line.
    Coils have the same face area.
    There is 200 more CFM on the 2.5 ton unit.
    The locked rotor amps are higher for the 2.5 ton unit.
    The 2.5ton requires a 25A fuse/circuit breaker. 25A breakers are an oddball size for many panels, I can't remember seeing any.
    The EER/SEER ratings are similar for both units, which makes me think the 2 ton would have to use less power since it has less output.
    Virginia
    probly has different run cap mfd
    30 , 35