    R-22 retrofits.

    Has anyone used the r-22a refrigerant .If so ,how did it turn out. Havent used it yet but i am debating due to the cost.I know its not ideal but for old equipment it could be ok i think Im referring to the superfreeze r22ahttp://www.super-freeze.com/super-freeze-22a-refrigerant-r22-freon-replacement-30-lb-equivalent-tank/ld

  2. #2
    Join Date
    Jul 2012
    Location
    Everett, WA
    Posts
    270
    Post Likes
    I know on a few the the RTU's at the one of the stores that our owner own's we have converted them over to MO99, the boss didn't wanna use Super Freeze after talking with one of the suppliers about which wa better. We changed out all the filter driers on all the units tha we converted over to MO99.

  3. #3
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by heresjohnnyb View Post
    Has anyone used the r-22a refrigerant .If so ,how did it turn out. Havent used it yet but i am debating due to the cost.I know its not ideal but for old equipment it could be ok i think Im referring to the superfreeze r22ahttp://www.super-freeze.com/super-freeze-22a-refrigerant-r22-freon-replacement-30-lb-equivalent-tank/ld
    I heard Honeywell is about to market a new r-22 substitute, compatible with mineral oil, no methane or propane on it and very small glide.
    I would advise the customer to wait or buy a new 410a unit, wouldn't use r-22a or mo99, they are loaded with flammables and the unit efficiency takes a big drop in the neighborhood of 30%, the few pennies you save by changing refrigerants become dollars wasted on energy consumption.

  4. #4
    Join Date
    Jul 2012
    Location
    Everett, WA
    Posts
    270
    Post Likes
    I asked why not just get a new 410a system, but the stores that we have retrofited to MO99 are a year or two from being remodeled and all new equipment, any way.

    Quote Originally Posted by valdelocc View Post
    I heard Honeywell is about to market a new r-22 substitute, compatible with mineral oil, no methane or propane on it and very small glide.
    I would advise the customer to wait or buy a new 410a unit, wouldn't use r-22a or mo99, they are loaded with flammables and the unit efficiency takes a big drop in the neighborhood of 30%, the few pennies you save by changing refrigerants become dollars wasted on energy consumption.

  5. #5
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    R-22a is a hydrocarbon blend.

    It's fine if you know how to properly handle and don't mind violating a few building codes.

    Can you properly identify ignition sources in the equipment? They're a bad idea with hydrocarbon refrigerants.

    You might find Hychill's experience with their "Minus 50" hydrocarbon blend of interest: http://www.tamahereforum.co.nz/wp-co...to-inquest.pdf
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  6. #6
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by Andy Schoen View Post
    R-22a is a hydrocarbon blend.

    It's fine if you know how to properly handle and don't mind violating a few building codes.

    Can you properly identify ignition sources in the equipment? They're a bad idea with hydrocarbon refrigerants.

    You might find Hychill's experience with their "Minus 50" hydrocarbon blend of interest: http://www.tamahereforum.co.nz/wp-co...to-inquest.pdf
    Andy, I enjoyed the article you wrote about it on RSES journal, very informative. thanks.

  7. #7
    Join Date
    Aug 2011
    Location
    Chicago
    Posts
    64
    Post Likes
    Read the article. I believe R290 is propane. Was told very popular in europe.ammonia is a lot safer than propane

  8. #8
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by valdelocc View Post
    Andy, I enjoyed the article you wrote about it on RSES journal, very informative. thanks.
    Thanks! R-22 was a very good refrigerant. It is much more difficult to replace than R-12.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  9. #9
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by Jimmyhat 597 View Post
    Read the article. I believe R290 is propane. Was told very popular in europe.ammonia is a lot safer than propane
    R-290 is propane, and it is now acceptable for use under the EPA SNAP rules.

    Only new equipment. No retrofits.

    Maximum charge per circuit under SNAP rules is only 150 grams. Only commercial refrigeration applications. And you have to know what you are doing with hydrocarbon refrigerants.

    Those who work on small commercial refrigeration systems... you will see this soon.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  10. #10
    Join Date
    Jun 2010
    Location
    Southwest NM
    Posts
    22
    Post Likes

    Minus 50 incident

    Quote Originally Posted by Andy Schoen View Post
    You might find Hychill's experience with their "Minus 50" hydrocarbon blend of interest: http://www.tamahereforum.co.nz/wp-co...to-inquest.pdf
    Quite a story there -- plenty of mis-application and some very unfortunate outcomes.

    http://www.epa.gov/greenchill/downlo...frigerants.pdf brought me up to speed a bit. Safety systems and controls are about to get a lot more complex.

  11. #11
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    Thanks for the feedback guys. I think im gonna keep breaking the customers banks for now just until there is a reliable solution for the 360 dollar a jug r-22

  12. #12
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    You may read a fine article on R-22 alternative refrigerants here: https://www.rses.org/assets/rses_jou...ompressors.pdf
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  13. #13
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    thanks andy

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •