Page 2 of 2 FirstFirst 12
Results 14 to 23 of 23
  1. #14
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    183
    so when it finishes defrost and switches back to condenser inside the left over heat in heat exchanger could cause a high pressure trip. Am I understanding that correctly?

  2. #15
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    183
    I would also like to add that if possible I think the indoor coil should be on the return side of furnace.

  3. #16
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    183
    Read back down through the thread and saw where been there said not to put coil in the return, what is the reasoning behind that?

  4. #17
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,194
    if the heat exchanger is too hot when it comes out of defrost, it can trip the HPS and lock out the heat pump.

    An evap coil in the return will cause condensation in the oil furnaces heat exchanger in the summer, and rot it out from the inside out. You also lose some of your heat pumps heat capacity to heating the chimney.
    Contractor locator map

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    183
    Quote Originally Posted by beenthere View Post
    if the heat exchanger is too hot when it comes out of defrost, it can trip the HPS and lock out the heat pump.

    An evap coil in the return will cause condensation in the oil furnaces heat exchanger in the summer, and rot it out from the inside out. You also lose some of your heat pumps heat capacity to heating the chimney.
    Thanks been there. As an inexperienced tech I appreciate the fact that you take the time to answer my questions. I feel blessed to be able to come here and ask questions and get answers from guys who are probably some of the best inn the trade, definitely a fortunate thing for younger technicians.

  6. #19
    Join Date
    Feb 2008
    Location
    Massachusetts
    Posts
    696
    Beenthere is not that great, he's just old and seen it all.

    Sent from my PC36100 using Tapatalk 2

  7. #20
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,194
    if you get to work on any gas/electric RTUs. look at how rusted out the heat exchangers get with the evap coil before the gas heat exchanger. It can be real eye opener as to how quickly a HE can rust out from condensate forming in the HE from the A/C.
    Contractor locator map

    How many times must one fix something before it is fixed?

  8. #21
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,194
    Quote Originally Posted by mlstark View Post
    Beenthere is not that great, he's just old and seen it all.

    Sent from my PC36100 using Tapatalk 2
    And bald. LOL
    Contractor locator map

    How many times must one fix something before it is fixed?

  9. #22
    Join Date
    Dec 2007
    Posts
    3,844
    Open forum, so do not want to get too detailed.

    As Beenthere said, evap in the supply above the oil HX, defrost limit switch, dual fuel stat with OD sensor AND move the original fan/limit switch if normal older style mechanical type.

    I have seen this several times this year, customer going on the cheap picking company and they melted the evap pan. Most likely cause, fan/limit switch in original spot and it allowing too high temp before activating( won't get anymore specific than that in this forum).

  10. #23
    Join Date
    Aug 2012
    Location
    Vancouver Island, British Columbia
    Posts
    16
    thanks for the input you guys this site is awesome

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •