Pretty new to I-VU. Got sent down to a location today. They are having issues with alarms spamming system and remote emails/phones.
General issue is any alarms coming from a few older 6400's will just keep populating. You can ack and/or delete them, but they just keep populating. The time stamps are from weeks ago. They are return to normal alarms. I tried removing the return to normal alarming, they still populate. The only way I can get it to stop is to disable the alarms.
Any idea? Sometimes you will get 3 of the same alarms. This is not happening with any of the rest of the controllers. And I manually tripped an alarm on these controllers and it now does the same thing.
-
08-15-2012, 05:56 AM #2
Regular Guest
- Join Date
- Mar 2010
- Posts
- 28
Use NSTV to determine where the Alarm Acknowledger is. While your at it, check to see that you have 1 Broadcast Ack per bus and only 1 time Broadcaster. It sounds like the controller that is re-sending the alarm is not getting a confirmation back from the Alarm Ack, so it just keeps resending.
-
08-16-2012, 05:06 PM #3
I was able to fix the alarm problem, by just restarting the controllers.
But I tried to get into the controllers with NSTV and it's a problem. I have the USB to CCN converter. I have all the drivers installed. The Link light is on. Status light in blinking. But Error light is on. I tried a RJ14 and RJ25 cable, both do the same thing. Both cables, I made and are straight pin to pin. I tried scan the bus, but found nothing. Opened up bus scan and all there is are collisions.
Any idea what I'm doing wrong?
-
08-17-2012, 07:43 AM #4
Regular Guest
- Join Date
- Mar 2010
- Posts
- 28
Need to check the basics. Need to have one (and only 1) Broadcast Ack on each Bus (including Bus 0). Need to have 1 time broadcaster and 1 Alarm Ack. If you don't have these setup, then you are going to ahve all kinds of problems on the 485-side.
What Controller are you connecting to? A 6400? If so, what is the Version of the Firmware?
-
08-17-2012, 09:54 AM #5
What are the alarms you are getting? There are no default alarms setup in i-Vu other that communications for a CC6400, all other alarms need to be setup and programmed in the CC6400.
As previously stated, what is the firmware? Some of the really older CC6400 need a firmware upgrade to be 100% compatible with i-Vu.
How are the alarms setup in the controller and in i-Vu? With i-Vu and CC6400's I have found that they work better if I allow i-Vu to handle the alarms. I turn off the Alarm Processing [ALMPROC] in the configuration so the CC6400 does not broadcast the alarms to the network. Then mapped the Alarm Status [STATUS] from the maintenance table. Once mapped to i-Vu, setup the alarm in i-Vu.
In addition to verifying the CCN acknowledger's as previously stated you can also check for the following acknowledger's in i-Vu, not sure if you have a Standard or Plus ....
In the system options under the General Tab are the following checked ...
1: Allow CCN Gateway to acknowledge alarms from CCN serial network
2: Allow CCN Gateway to acknowledge alarms for CCN/IP network
If a Plus, also look at the Ethernet & CCN Alarm Acknowledger's in the Router/Link "User Config Table", the are ALRMACK1 & ALRMACK2.
Originally Posted by Qui-Gon Jinn (Star Wars Episode 1)
-
08-17-2012, 02:16 PM #6
These controllers are 6400's with 2 I/O's each. The revision is 6.
My problem is I can get the usb to ccn converter to work. Like I said the converter is showing a error light.
-
08-17-2012, 05:46 PM #7
Any time Ive had the error light come on it was a problem on the bus... a short or damaged device ect. Plug into the 6400 and disconnect the it from the bus and see if that helps you
-
08-17-2012, 05:57 PM #8
One other question......the version of NSTV I have is 2.02. Is that the most current version?
Looking through some older posts.....there was mention of a 2.2 version?
I also can't get on hvacpartners....my company's login constantly needs to be reset, because other techs don't disable popups and try to log in multiple times.
-
08-20-2012, 05:56 PM #9
A little update.......I had to go to another site today. They had a 3v VVT zoning system. After some messing around, I ended up trying a cable from one on the telephones in the office. And it worked. I was making my cables wrong.
So I ended up getting some time to go back to the OP job. The one controller I kept trying to connect to still didn't work. So I tried another. Finally was able to see the controllers.
So that leads me to my next question.........I got an error message, while uploading some on the 6400 controllers. Here's a screenshot-