Thread: moisture, or just impatient?

  1. #21
    Join Date
    Aug 2012
    Location
    Hot Springs, Arkansas, United States
    Posts
    55
    Post Likes
    Does your vacuum pump have a gas ballast port? This is from Yellow Jacket U If you suspect an open or wet system, be sure to use the gas ballast feature on your vacuum pump. The gas ballast prevents water vapor from condensing in the vacuum pump oil by introducing a small amount of fresh air into the pumping chamber. Open the gas ballast just slightly and then begin to watch your electronic vacuum gauge. If the vacuum stays at a consistently high level of microns or doesn’t pull down below 5,000 microns, your system still contains contamination or has a leak. Repair the leak before proceeding.

  2. #22
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    If your hitting 500 micron and can hold it , or at least under 700 for 1/2 hr I'd say you have clean tight system. Doesn't matter how long it takes to get there as long as it gets there. As previously stated your 410A systems will take longer, much longer in some cases, then the R22 systems with MO. POE likes liquid be it refrigerant or water. Once it gets ahold of some it will not let it go without a long hard fight. Your procedures sound good and proper so relax and be patient. On a side note I like to use brute manifold set with 3/8 hose. Get a vac pump with a 3/8 connection and pull through it. Will make a big difference in pull down time.

  3. #23
    Join Date
    Aug 2012
    Posts
    60
    Post Likes
    Thread Starter
    Quote Originally Posted by Thorazine View Post
    Does your vacuum pump have a gas ballast port? This is from Yellow Jacket U If you suspect an open or wet system, be sure to use the gas ballast feature on your vacuum pump. The gas ballast prevents water vapor from condensing in the vacuum pump oil by introducing a small amount of fresh air into the pumping chamber. Open the gas ballast just slightly and then begin to watch your electronic vacuum gauge. If the vacuum stays at a consistently high level of microns or doesn’t pull down below 5,000 microns, your system still contains contamination or has a leak. Repair the leak before proceeding.
    I've always achieved 300-500. I don't think I have any leaks.

    Quote Originally Posted by Tommy knocker View Post
    If your hitting 500 micron and can hold it , or at least under 700 for 1/2 hr I'd say you have clean tight system. Doesn't matter how long it takes to get there as long as it gets there. As previously stated your 410A systems will take longer, much longer in some cases, then the R22 systems with MO. POE likes liquid be it refrigerant or water. Once it gets ahold of some it will not let it go without a long hard fight. Your procedures sound good and proper so relax and be patient. On a side note I like to use brute manifold set with 3/8 hose. Get a vac pump with a 3/8 connection and pull through it. Will make a big difference in pull down time.
    I was concerned of my method to keep vacuum sterile. I guess without oversized hose, it'll be turtle slow. Company wont budge on equipment. I had to fight to get a new pump, because a coworker dumped 10w-40 in it....

    Yeah.....




    Sent from my PC36100 using Tapatalk 2

  4. #24
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    Why not buy your own tools, that way you can take them with you and no one else can mess with them?

  5. #25
    Join Date
    Aug 2012
    Posts
    60
    Post Likes
    Thread Starter
    Quote Originally Posted by syndicated View Post
    Why not buy your own tools, that way you can take them with you and no one else can mess with them?
    I was hired to replace sinks and buff drywall repairs. Handbook said basic tools required. They want hvac fixed, they can fork out some hardware my opinion anyways.
    Sent from my PC36100 using Tapatalk 2

  6. #26
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Your methods look good but I would blow out all of the nitrogen before you hook up the vacuum pump. Your not going to get any moisture going into your system through your 2 hoses and manifold by letting all the nitrogen out.

  7. #27
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by XcelTech View Post
    I use to have a Robinair 6 CFM. I hated the thing. I suggest you buy a more reliable vacuum pump. It is expensive but you will get your moneys worth. Buy the Appion TEZ8 and the MegaFlow Speed kit.
    how about running a piece of tubing all the way to the stratosphere? the best vacuum pumps are free and highly reliable.

  8. #28
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by valdelocc View Post
    how about running a piece of tubing all the way to the stratosphere? the best vacuum pumps are free and highly reliable.
    Wouldn't work.

    You would have no suction at all on the bottom of that tube.

  9. #29
    Join Date
    Oct 2010
    Location
    Austin, TX
    Posts
    1,381
    Post Likes
    I find that free is a German word for doesn't work and will make your day a living hell.
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.

  10. #30
    Join Date
    Feb 2012
    Location
    PA
    Posts
    30
    Post Likes
    Vac pump oil breaks down because of contaminants, heat, etc.. You're not helping your pump by using it to pull nitrogen out.. Also, the rotary vanes aren't supposed to be exposed to positive pressure.. Let your nitrogen blow before starting pump, you wont be introducing contaminants.. I used to abuse my pumps and learned that if you show it some love it'll return the favor , in the form of making a job much less stressful..

  11. #31
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    Wouldn't work.

    You would have no suction at all on the bottom of that tube.
    I tried once and got down to 500 microns in 2 minutes and 55 seconds, dont need no super duper mighty vacuum thingy.

  12. #32
    Join Date
    Aug 2012
    Posts
    60
    Post Likes
    Thread Starter
    Quote Originally Posted by ndk1911 View Post
    Vac pump oil breaks down because of contaminants, heat, etc.. You're not helping your pump by using it to pull nitrogen out.. Also, the rotary vanes aren't supposed to be exposed to positive pressure.. Let your nitrogen blow before starting pump, you wont be introducing contaminants.. I used to abuse my pumps and learned that if you show it some love it'll return the favor , in the form of making a job much less stressful..
    15-20# tops.,and I tease the valves at first, I don't whip them wide open from the get go.

    Sent from my PC36100 using Tapatalk 2

  13. #33
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    steal there tools .....lol
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  14. #34
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Actually there are a few devices you can attach to your vacuum pump that will actually allow your pump to " give you love ".

    You just won't find them at johnson supply.

  15. #35
    Join Date
    Aug 2010
    Posts
    4,338
    Post Likes
    Quote Originally Posted by valdelocc View Post
    how about running a piece of tubing all the way to the stratosphere? the best vacuum pumps are free and highly reliable.
    It would work as well as sticking a 1000' pipe into the ocean and expecting water to come gushing out at the top. After all, the pressure gets higher at depth right? It works the same way with air. It just takes more distance to develop the same pressure gradient since air weighs nowhere near as much as water.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •