Results 1 to 8 of 8
  1. #1
    Join Date
    Aug 2012
    Posts
    2
    Post Likes

    I ordered a 3.5-5 ton Goodman TXV

    I have the same senario with the exact same P/N condenser and a Goodman 3.5 ton ARUF air handler. The system is cooling, pressures look good, but cannot satisfy below 79 degrees in the heat of the day (central Florida, summer). I just ordered a Goodman 3-5 ton TXV kit. Did the TXV resolve your issue?

  2. #2
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    530
    Post Likes
    you should have a txv to match the outdoor unit (capacity and refrigerant type)

  3. #3
    Join Date
    Aug 2012
    Posts
    2
    Post Likes
    Thread Starter
    Quote Originally Posted by ADillon View Post
    you should have a txv to match the outdoor unit (capacity and refrigerant type)
    Great, I ordered a 3.5-5 ton Goodman TXV for R-22 based on advise from another more experienced tech. The outdoor unit is a 3 ton R-22 unit. What will be the outcome of using this 3.5-5 ton TXV?

  4. #4
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,733
    Post Likes
    Quote Originally Posted by jroper630 View Post
    Great, I ordered a 3.5-5 ton Goodman TXV for R-22 based on advise from another more experienced tech. The outdoor unit is a 3 ton R-22 unit. What will be the outcome of using this 3.5-5 ton TXV?
    It might overfeed the evaporator. It might not. If you install it and don't check superheat or subcooling, you'll never know if it is or not.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  5. #5
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    530
    Post Likes
    Quote Originally Posted by jroper630 View Post
    Great, I ordered a 3.5-5 ton Goodman TXV for R-22 based on advise from another more experienced tech. The outdoor unit is a 3 ton R-22 unit. What will be the outcome of using this 3.5-5 ton TXV?
    I don't know goodman usually there is a txv that does a variety of sizes like 1.5-3 ton then it steps up to another txv that does 3.5-4 and then another that does 5. just as an example. So if you are using the next size up from what you need, it might overfeed. It is hard to tell what the outcome will be with mix matched units

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,513
    Post Likes
    Made this its own thread. You are not allowed to post in other peoples threads, in the AOP forums. please read our site rules, thank you.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    6,986
    Post Likes
    On the Goodmana's some of the txv's need to be adjusted . It does take some time and effort

  8. #8
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    6,670
    Post Likes
    the outcome is not good.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted